had to use my strippers to to grab it .
They we're flush until 3" of foam and siding was added around them.the siding has trapped the base of the cover . View attachment 9543
And the cover is designed to be installed sideways?
(B) Installation and Use. Listed or labeled equipment
shall be installed and used in accordance with any instructions
included in the listing or labeling.
Picture is sideways recep is vertical Doing this on my phone
View attachment 9544
Flip cover is installed correctly. Some of the other ones are filling up with snow that's blowing in
Around here you can't get a siding permit without an electrician pulling an electrical permit to take care of the service, outside lights and receptacles.
Is it my bad eyes or is that receptacle mounted to that box with nothing more than a gasket as protection?
What the heck kind of cover is that? How does it attach to the box?
And the cover is designed to be installed sideways?
(B) Installation and Use. Listed or labeled equipment
shall be installed and used in accordance with any instructions
included in the listing or labeling.
Picture is sideways recep is vertical Doing this on my phone
What are you going to do to correct these "sunken" boxes?
What code section prohibits that "sunken" condition?
Though it may be a PITA to change a receptacle I see nothing wrong with it.
WP while in use cover is a different issue, and may be a problem should you decide to try to use one.
If the cover was a non WP while in use before siding work was done, it may very well have been compliant at time of original installation. If local rules require upgrading it to WP while in use then fine, but otherwise I don't see why it needs upgraded.
And I disagreed with post #12 and still do.My post #12.
I believe that the OP said the siding was added.
I'm going with 314.20 Heck there's only 31 of them to fix and the temperature should climb into the -20s this week
My post #12.
I believe that the OP said the siding was added.
Being that the box is now in a cubby hole so to speak is not the same thing that is being addressed by 314.20.
That makes me a little short of breath just reading it.When I was younger I have crawled in spaces that were ~ 1 cinder block high...
Exactly what my disagreement is based on, and better worded than what I came up with, thanks.
And in the picture the same is true.But in a cubbyhole, stage pocket or floor receptacle it is still possible to remove the device and access the interior of the box without removing wall finish!
I believe that at one point the OP stated that it was not.And in the picture the same is true.
Roger