ramsy
Roger Ruhle dba NoFixNoPay
- Location
- LA basin, CA
- Occupation
- Service Electrician 2020 NEC
Get the App, and try it yourselfWhat are you using for a k value? and what do you get for #4 AL?
Get the App, and try it yourselfWhat are you using for a k value? and what do you get for #4 AL?
Was the the question Short Circuit and not Ground Fault?
Yes OP said 480/277 was available at the source end, probably much more than a 1 kVA transformer as well so source impedance is less consideration than circuit length resistance. Line to neutral/ground fault in this situation should have less fault current than line to line fault and would mean longer clearing time for overcurrent protection. 41 amps on a 20 amp breaker will seem like it takes an eternity to trip compared to having same fault near the source where a few thousand amps might flow during the incident.Op was using 480. Not sure about L-N worse case SCA with Y xfmr.
L-N maybe worse case SCA for short runs of center tap 120/240v
Does GFPE circuit breaker instructions inform us of distance limits from capacitance, or is this published elsewhere?..If you have a huge long run, with a small load and wire sized for voltage drop at the expected load current.. ..ground fault detection rather than overcurrent protection _is_ the best approach.
The 60A breaker would prevent damage on a #4 AL, but a ground wire could be over-stressed in a sustained L-G fault if it's a smaller gauge than this. That's where the ground fault protection Jon mentioned could help. It would need to have a relatively high trip level to tolerate the capacitance of a 6500 ft. run, as was brought up earlier.If the OP installed 6500' of #4 AL and it was on a 2 pole 60 a L-G fault would never trip.
Even at 86 amps it might take a while.
Yes, it can, but it’s also required in places so it is an acceptable risk.Keep in mind electronic GF protection can fail.
Yes, it can, but it’s also required in places so it is an acceptable risk.
Are we missing one?Required in places in conjunction with an EGC.
Are we missing one?
This superior design won the bid. Bid losers are just arguing over alternative designs.I still think it's silly to run a feeder almost 1-1/4 miles IF a solar-and-battery solution could work.
Now your the SCA master.using this http://www.cooperindustries.com/content/public/en/bussmann/electrical/resources/fc2.html
I used 2% for the Z gives me:
Itotal s.c. (L-L) 86 AMPS
Is.c. (L-N) 43 AMPS
V (L-L) 480 V
for #4 AL.
If the OP installed 6500' of #4 AL and it was on a 2 pole 60 a L-G fault would never trip.
Even at 86 amps it might take a while.
I guess this is where 110.10 comes into play enforcing voltage drop.
Now your the SCA master.
Since IEEE standard for Short Ckt. Analysis uses 0.85 pf, all you need is a Voltage Drop calculator that can adjust Power Factor.
NEC Chap. 9. Table 9 shows R and X conductor values, and a formula for effective Z in Tbl.9, based on those table properties, assuming pf=0.85.Why not use the R and X values for the circuit run added to that of the source?
NEC Chap. 9. Table 9 shows R and X conductor values, and a formula for effective Z in Tbl.9, based on those table properties, assuming pf=0.85.
NEC Table 9 selections between PVC and Steel raceway Reactance (X) appear to affect impedance (Z) much less than changes in power factors. Yet no verified and validated calculator has been found for free, beyond those based on NEC tables fixed on pf=0.85, or worse K factors with unity pf=1.
No, you’re not.I'd be curious to know if the equipment being fed is all multi-voltage capable. Sometimes these types of equipment can be fed any 50-60HZ voltage between 120 and 277 with no ill effects. Voltage drop is a FPN in the code anyway...so 5% is not a hard requirement....just a suggestion. So if the load is, say, all electronic equipment and LED lighting with the multi-volt type power requirements...then a 20-30% drop may still get the job done. Am I missing something here?