Might I suggest that for the 24" thing kind of reverse things and ask his explanation of the 210.52(C)(1) requirement. And not be being disrespectful but say you want to learn. Kind of K.A. but gets away from butting heads, and feeding his EGO.
AFA the SER cable touching the concrete, only thing I could think of that would be a issue is if you were unable to secure the cable within 12" of entry to the box, 230.51(A)
AFA the SER cable touching the concrete, only thing I could think of that would be a issue is if you were unable to secure the cable within 12" of entry to the box, 230.51(A)

first one was the kitchen counter outlet was within 24” of the kitchen sink. The second one was I used SER cable for the service. The ceilings in the basement are fairly high for around here. They are about 8’ ceilings. I came in with my SER installed plywood to the wall and secured the SER before it entered the panel. However since it is in about 2-3’ of contact with the cement foundation before it hits the plywood that is against code and said I need to install a 2x4 going vertical to protect the SER from touching the foundation…. I knew he would find something to fail me for since I’m an out of town electrician.