Good catch - the 2020 does have a G beside the fridge outlet. That's the only difference I've noticed, thus farmust be old code. refrigerator would be required to be gfci protected in this layout now...
Good catch - the 2020 does have a G beside the fridge outlet. That's the only difference I've noticed, thus farmust be old code. refrigerator would be required to be gfci protected in this layout now...
You should be able to tell by the content of the book if it's the 2020 or not. Cover is not needed. But I guess some people look at the content differently. Me, I found it at the bottom of the page right away.The outlets in the exhibit are in the same location in the 2020 NEC Handbook. But the counter is a bit three dimensional and has a brown or wood looking floor.
Just thought I'd throw that out there. I had to look for the cover to it to make sure it's the 2020 book. Having no cover should've been enough to convince me.![]()
Why would the 2020 require the kitchen fridge to be GFCI protected? Have I missed something in my research? It would only be GFCI protected if it's taken off the SABC.Good catch - the 2020 does have a G beside the fridge outlet. That's the only difference I've noticed, thus far
Because it is with 6' of a sink. Whether it is on an individual branch circuit or the SABC is not relevant.Why would the 2020 require the kitchen fridge to be GFCI protected? Have I missed something in my research? It would only be GFCI protected if it's taken off the SABC.
But that's not something new to 2020... GFCI protection requirements were expanded, but as far as the kitchen is concerned, it's still limited to receptacles that serve the countertops as far as I'm aware.Because it is with 6' of a sink. Whether it is on an individual branch circuit or the SABC is not relevant.
The NECH as you know includes the exact text of the NEC which is legally enforceable. The commentary is just that and just the authors opinion and is not to be considered part of the code or enforceable.Are you implying that the Handbook (i.e. NECH) LACKS information that the NEC contains? Because that would be a pretty messed up thing to do to people who are trying to understand the code.
That is a common explanation and does seem logical, don't know if that is actually why or not. Would have to find copies of proposals and comments from the CMP way back whenever this rule was added to really know what might been behind it.Well the receptacle to the left of the sink would prove the inspector wrong. I don't see how that could be misinterpreted.
Unless you're saying he misunderstood the receptacles by the stove in the exhibit that show a 2ft spacing and thought that meant a minimum, whereas it's actually a maximum.
Correct me if I'm wrong, but I believe it's common knowledge that most countertop appliances feature a 2ft cord and that's the reason for this requirement... so that an appliance placed anywhere on countertop can reach a receptacle. At least, that's how it was explained to me way, way back in the day.
It is no more or less relevant than an explanation on this forum, by Mike Holt himself, IAIEI or any other professional person/organization that creates similar material. Most of them will have similar explanations on most content, but none of them are official representatives of NFPA. They are just saying it, drawing it, etc. the way they interpret things.The illustration is commentary, no need to read any further.
Correct!It is no more or less relevant than an explanation on this forum
2011 specifically said in areas other than kitchens in the part that mentioned 6 feet from sinks.But that's not something new to 2020... GFCI protection requirements were expanded, but as far as the kitchen is concerned, it's still limited to receptacles that serve the countertops as far as I'm aware.
Edit time expired: since 2014 any receptacle within any sink been required to be GFCI protected.2011 specifically said in areas other than kitchens in the part that mentioned 6 feet from sinks.
2014 took that wording out and within 6 feet of all sinks has been the rule since.
Receptacle serving any kitchen counter top been required to be GFCI protected since I believe 1996
Roger that. I was merely responding to @Buck Parrish who claimed the 2020 added a G besides the fridge outlet and questioning what in the 2020 would have prompted that change.2011 specifically said in areas other than kitchens in the part that mentioned 6 feet from sinks.
2014 took that wording out and within 6 feet of all sinks has been the rule since.
Receptacle serving any kitchen counter top been required to be GFCI protected since I believe 1996
The "G" somewhat irrelevant if the commentary is about receptacle placement, but yes nothing wrong with making that right within content intended to illustrate other aspects.Roger that. I was merely responding to @Buck Parrish who claimed the 2020 added a G besides the fridge outlet and questioning what in the 2020 would have prompted that change.
Makes you wonder if the authors of the NEC missed this in the 2014. Should the aforementioned exhibit have had a G besides the fridge outlet because of the 6 foot rule in the 2014? Because it's not in my copy of the '14. But it's just commentary right, so doesn't matter if they got it wrong? lol
Message received: You're born alone and you die alone, clutching the NEC in your coffin, lol. (duude, that was dark)
True however what year to take with ya.Message received: You're born alone and you die alone, clutching the NEC in your coffin, lol. (duude, that was dark)
Hopefully the 2086 Ed. lol.True however what year to take with ya.![]()
Wasn't always every three years and maybe someday will be different again?Hopefully the 2086 Ed. lol (Have fun counting to see if I did that right, lol)
Might I suggest that for the 24" thing kind of reverse things and ask his explanation of the 210.52(C)(1) requirement. And not be being disrespectful but say you want to learn. Kind of K.A. but gets away from butting heads, and feeding his EGO.
AFA the SER cable touching the concrete, only thing I could think of that would be a issue is if you were unable to secure the cable within 12" of entry to the box, 230.51(A)
Bills to pay my friend. Bills to pay. Unfortunately.I had a friend who was an inspector. His pet peeve was electricians calling him wanting him to tell them how to do the job because they wouldn't even attempt to use the code book. He didn't mind a few questions. But many asked him stuff they should have known.