Fall Protection?
joebell
New Hampshire
I attended a contractor EHS meeting for one of our customers today. One of the topics of discussion was OSHA's requirements for fall protection on heights above 6'. One of the contractors said that this rule applies to step ladders as well as staging etc.
Is this the case? I have never heard of this rule for step ladders.
I recently attended a seminar on scaffold safety and from what I remember it does not pertain to step ladders. I have seen GC's try to enforce their own 6' rule for step ladders.
Not the way I have heard the law - It's a royal PITA on bigger projects.
FALL PROTECTION SYSTEMS CRITERIA AND PRACTICES
Guardrail Systems
If the employer chooses to use guardrail systems to protect workers from falls, the systems must meet the following criteria. Toprails and midrails of guardrail systems must be at least one-quarter inch (0.6 centimeters) nominal diameter or thickness to prevent cuts and lacerations. If wire rope is used for toprails, it must be flagged at not more 6 feet intervals (1.8 meters) with high-visibility material. Steel and plastic banding cannot be used as toprails or midrails. Manila, plastic, or synthetic rope used for toprails or midrails must be inspected as frequently as necessary to ensure strength and stability.
The top edge height of toprails, or (equivalent) guardrails must be 42 inches (1.1 meters) plus or minus 3 inches (8 centimeters), above the walking/working level. When workers are using stilts, the top edge height of the top rail, or equivalent member, must be increased an amount equal to the height of the stilts.
Screens, midrails, mesh, intermediate vertical members, or equivalent intermediate structural members must be installed between the top edge of the guardrail system and the walking/working surface when there are no walls or parapet walls at least 21 inches (53 centimeters) high. When midrails are used, they must be installed at a height midway between the top edge of the guardrail system and the walking/working level. When screens and mesh are used, they must extend from the top rail to the walking/working level and along the entire opening between top rail supports. Intermediate members, such as balusters, when used between posts, shall not be more than 19 inches (48 centimeters) apart.
Other structural members, such as additional midrails and architectural panels, shall be installed so that there are no openings in the guardrail system more than 19 inches (48 centimeters).
The guardrail system must be capable of withstanding a force of at least 200 pounds (890 newtons) applied within 2 inches of the top edge in any outward or downward direction. When the 200 pound (890 newtons) test is applied in a downward direction, the top edge of the guardrail must not deflect to a height less than 39 inches (1 meter) above the walking/working level.
Midrails, screens, mesh, intermediate vertical members, solid panels, and equivalent structural members shall be capable of withstanding a force of at least 150 pounds (667 newtons) applied in any downward or outward direction at any point along the midrail or other member.
Guardrail systems shall be surfaced to protect workers from punctures or lacerations and to prevent clothing from snagging.
The ends of top rails and midrails must not overhang terminal posts, except where such overhang does not constitute a projection hazard.
When guardrail systems are used at hoisting areas, a chain, gate, or removable guardrail section must be placed across the access opening between guardrail sections when hoisting operations are not taking place.
At holes, guardrail systems must be set up on all unprotected sides or edges. When holes are used for the passage of materials, the hole shall have not more than two sides with removable guardrail sections. When the hole is not in use, it must be covered or provided with guardrails along all unprotected sides or edges.
If guardrail systems are used around holes that are used as access points (such as ladderways), gates must be used or the point of access must be offset to prevent accidental walking into the hole.
If guardrails are used at unprotected sides or edges of ramps and runways, they must be erected on each unprotected side or edge.
Personal Fall Arrest Systems
These consist of an anchorage, connectors, and a body belt or body harness and may include a deceleration device, lifeline, or suitable combinations. If a personal fall arrest system is used for fall protection, it must do the following:
Limit maximum arresting force on an employee to 900 pounds (4 kilonewtons) when used with a body belt;
Limit maximum arresting force on an employee to 1,800 pounds (8 kilonewtons) when used with a body harness;
Be rigged so that an employee can neither free fall more than 6 feet (1.8 meters) nor contact any lower level;
Bring an employee to a complete stop and limit maximum deceleration distance an employee travels to 3.5 feet (1.07 meters); and
Have sufficient strength to withstand twice the potential impact energy of an employee free falling a distance of 6 feet (1.8 meters) or the free fall distance permitted by the system, whichever is less.
As of January 1, 1998, the use of a body belt for fall arrest is prohibited.
Personal fall arrest systems must be inspected prior to each use for wear damage, and other deterioration. Defective components must be removed from service. Dee-rings and snaphooks must have a minimum tensile strength of 5,000 pounds (22.2 kilonewtons). Dee-rings and snaphooks shall be proof-tested to a minimum tensile load of 3,600 pounds (16 kilonewtons) without cracking, breaking, or suffering permanent deformation.
Snaphooks shall be sized to be compatible with the member to which they will be connected, or shall be of a locking configuration.
Unless the snaphook is a locking type and designed for the following connections, they shall not be engaged (a) directly to webbing, rope or wire rope; (b) to each other; (c) to a dee-ring to which another snaphook or other connecter is attached; (d) to a horizontal lifeline; or (e) to any object incompatible in shape or dimension relative to the snaphook, thereby causing the connected object to depress the snaphook keeper and release unintentionally.
OSHA considers a hook to be compatible when the diameter of the dee-ring to which the snaphook is attached is greater than the inside length of the snaphook when measured from the bottom (hinged end) of the snaphook keeper to the inside curve of the top of the snaphook. Thus, no matter how the dee-ring is positioned or moved (rolls) with the snaphook attached, the dee-ring cannot touch the outside of the keeper, thus depressing it open. As of January 1, 1998, the use of nonlocking snaphooks is prohibited.
On suspended scaffolds or similar work platforms with horizontal lifelines that may become vertical lifelines, the devices used to connect to a horizontal lifeline shall be capable of locking in both directions on the lifeline.
Horizontal lifelines shall be designed, installed, and used under the supervision of a qualified person, as part of a complete personal fall arrest system that maintains a safety factor of at least two. Lifelines shall be protected against being cut or abraded.
Self-retracting lifelines and lanyards that automatically limit free fall distance to 2 feet (0.6 l meters) or less shall be capable of sustaining a minimum tensile load of 3,000 pounds (13.3 kilonewtons) applied to the device with the lifeline or lanyard in the fully extended position.
Self-retracting lifelines and lanyards that do not limit free fall distance to 2 feet (0.61 meters) or less, ripstitch lanyards, and tearing and deforming lanyards shall be capable of sustaining a minimum tensile load of 5,000 pounds (22.2 kilonewtons) applied to the device with the lifeline or lanyard in the fully extended position.
Ropes and straps (webbing) used in lanyards, lifelines, and strength components of body belts and body harnesses shall be made of synthetic fibers.
Anchorages shall be designed, installed, and used under the supervision of a qualified person, as part of a complete personal fall arrest system that maintains a safety factor of at least two, i.e., capable of supporting at least twice the weight expected to be imposed upon it. Anchorages used to attach personal fall arrest systems shall be independent of any anchorage being used to support or suspend platforms and must be capable of supporting at least 5,000 pounds (22.2 kilonewtons) per person attached.
Lanyards and vertical lifelines must have a minimum breaking strength of 5,000 pounds (22.2 kilonewtons).
Positioning Device Systems
These body belt or body harness systems are to be set up so that a worker can free fall no farther than 2 feet (0.6 meters). They shall be secured to an anchorage capable of supporting at least twice the potential impact load of an employee's fall or 3,000 pounds (13.3 kilonewtons), whichever is greater. Requirements for snaphooks, dee-rings, and other connectors used with positioning device systems must meet the same criteria as those for personal fall arrest systems.
step ladders
step ladders
The 6 foot rule applies to step ladders. So any step ladder. 8 foot or larger you will have to have a harness on and anchored off to an overhead anchor point that is rated for 5000 pounds. Harness belts became illegal in 1998!! So basically a 2 day job could last 2 weeks!:smile:
I'm not saying break the law, I'm just saying plan accordingly, and don't be stupid. If risk were great enough wouldn't go there, with a harness, or not! You have to trust my judgement to act accordingly, for the conditions.
Edit to add - Better not drag a job out two weeks for a quick shot either!
Where does it say step ladders? The stuff that Rocky posted appear to apply to scaffolds.
Rob, it doesn't matter how you get six feet off the ground, if you fall and die, your still dead!
S yes, ladders are included. You would be amazed at how many people die from falling from ladders.
edit - go here for some ladder deaths.
Third death at City Center (before I left) was a fall from a ladder. Wasn't the intial fall that killed him, it was the other four floors of free fall that he fell from on the ladder.
I still don't agree and have yet to see documentation stating otherwise. A stepladder is not a scaffold.
Maybe someone will post the actual OSHA article and end the rumors and speculations ...
Stand by - getting the documentation.
OSHA LINK
It's a PDF so it won't copy. It's a 43 page document. Start at page 7 and read to page 10.
It doesn't matter what you or I think, it's the law.
How did you know what to put in the google box? Knew it was the law, just a matter of hunting down the documentation.
The OSHA fall protection rules do not apply to portable ladders.
If these ladders do not fit the definition of fixedladders as defined above, they would be deemed as portable ladders, and, therefore, not required to have fall protection. if they are fixed ladders, they are required to have fall protection at a length of 24 feet. (OSHA proposed rule 29 CFR 1910.23(c)(14)). Such a determination would have to be made on a case-by-case basis, per inspection. The proposed rule also provides for exemption from fall protection requirements for "qualified climbers" as provided in 1910.32(b)(5).
Source for above
lucky
lucky
Just was lucky in the search!:smile: These new regs just were adopted recently. I would guess that this is one of the most misunderstood job-site safety issues right now! Oh also the workin' it HOT thing maybe right there with this!:D If this is enforced, and I am sure it will be, you better take the time added to the smallest of jobs in consideration on bidding!:smile::smile:
My ears have burned for years as to the "Where's your harness?" noise. Don't get me going on too much government interference the government creates... be here a week :).
Don - out west here it does according to 99.9% of the contractors and my link. If it doesn't, please provide documentation so that I can carry it on jobs and get the correct word out.
OSHA LINK
From page 3 of the document (9 on the pdf page number).
Requirements to provide fall protection for workers on scaffolds
and ladders and for workers engaged in steel erection of
buildings are covered in other subparts of OSHA regulations.
The standard that this document is about does not apply to ladders.
Also take a look at page 15 of the document(21 on the pdf page number). Also look at the definition of "walking/working surface" on page 26 (32 pdf).