Fastening NM Boxes

Status
Not open for further replies.

triphase

Senior Member
05' NEC 314.23(B)(1) Would it be allowable "Let's say" to fasten a Nonmetallic box (In a tight location where normal manufacturer installed fastening is not possible) with screws toward the front edge interior? I see this a lot and have done this before. What are your interpretations? Thanks.
 
Re: Fastening NM Boxes

Bryan. Also, their are no "threads" of screws visible just the heads, approx. 1" back from front edge of box. Sorry, I do not have a picture available so will try do be as descriptive as I can. Thanks.
 
Re: Fastening NM Boxes

I have done this using round head screws although technically not allowed as the intent of this section I believe is to prevent conductor insulation damage from exposed metal fasteners.
 
Re: Fastening NM Boxes

There is a box called "SMART BOX" the screws appear to be in a recessed molded stud in the rear of the box.
 
Re: Fastening NM Boxes

I have done this many times and have never been questioned about it. You could use one of those adjustable boxes at six times the cost I suppose.

Paul
 
Re: Fastening NM Boxes

Here is one such box:


whnew78a.jpg



Here's a link for more info:

http://www.aifittings.com/whnew78.htm


I think that the head of the screw argument is lame. Metal boxes have 10/32 screws holding in a metal clamp and these don't seem to compromise the wiring.
 
Re: Fastening NM Boxes

Do You think it is more of a structural mounting intent of the code considering no exposed threads of screws or shanks of nails or bonding of exposed metal parts? Heck, I don't know ?
 
Re: Fastening NM Boxes

Originally posted by infinity:
I think that the head of the screw argument is lame. Metal boxes have 10/32 screws holding in a metal clamp and these don't seem to compromise the wiring.
Accidental contact of a bare conductor with a screw in a metal box would open the OCPD. (assuming the box is properly bonded). This would not happen in a non-metallic box. You would end up with an energized screw. :( Thats why the rules are so restrictive for plastic boxes.
 
Re: Fastening NM Boxes

This would not happen in a non-metallic box. You would end up with an energized screw. Thats why the rules are so restrictive for plastic boxes.
An energized screw going nowhere, except into a wood stud. So what makes the Smart Box legal, couldn't the same thing happen if I was to use the Smart Box.
 
Re: Fastening NM Boxes

I believe this is another case of thinking the NEC says something it does not actually say.

314.23(B) does not have different rules for metallic and non-metaliic boxes. There is one set of rules regardless what the enclosure is constructed of.

Screws and nails that PASS THROUGH (from the outside of one wall, through the box, and exiting the opposite wall) the box must be placed in an area that does not interfer with the mounting of a device into the box/enclosure. This is the part of the reason for the requirement that these items be located not more than than 1/4" from the back or ends (top and bottom) of the box. The only special provision for screws is that only exposed threads must be covered.

I can find nothing in the code that addresses screws that do not pass all the way through a box. For screws that start in the box and exit only one wall, there is nothing that says they even need to be bonded. For example look at an old-work box with internal mounting clamp screws or one with cable clamp screws.
 
Re: Fastening NM Boxes

Originally posted by jim dungar:
I can find nothing in the code that addresses screws that do not pass all the way through a box.
:cool:

Jim I have brought this up before and no one seemed to see it that way. I agree with you entirely.

IMO these screws..

mountingbox1.jpg


...do not pass through the box and therefore are not covered by 314.23(B) at all.

This next picture shows nails passing through the box that 314.23(B)(1) allows.

mountingbox3.jpg


And finally nails passing through a box that 314.23(B)(1) prohibits.

mountingbox2.jpg
 
Re: Fastening NM Boxes

Jim, "I tip my hat to you" you are correct. I do not see where this differs between NM and metal boxes.
 
Re: Fastening NM Boxes

Bob
Did you drill the holes or are those factory holes?? The ones with the nails. I did not think boxes like this were still made :confused:

Box number complies.
edit: box number one complies.

[ January 16, 2006, 02:02 PM: Message edited by: sandsnow ]
 
Re: Fastening NM Boxes

Originally posted by sandsnow:
Did you drill the holes or are those factory holes?? The ones with the nails.
No drilling.

They are just old works I had in my basement, they are no more than a couple years old.
 
Re: Fastening NM Boxes

But if you are going to bring up the "pass through the box" vs. not passing through the box, then any nail or screw that doesn't pass through th ebox doesn't comply. 314.23 gives you two ways of mounting a box with nails or screws:
1) Brackets on the outside, or
2) Nails and screw that "pass through the box" and meet the 1/4 rule.

I'm not saying I like what I am saying, but that is the way I read it. :(
 