FAULT CURRENT/ARC FLASH STUDIES

Scenario
Equipment old-no listed series combination
Upstream impedance, no-space constraint

240.86(A) not avoid then
The SCCR of equipment and the AIC of protective devices can only come from manufacturers.
Redesigning the power circuits or systems in order to reduce the available fault current is not what 240.86 means when it gives approval for an engineered solution stamped by a PE.
 
The SCCR of equipment and the AIC of protective devices can only come from manufacturers.
Redesigning the power circuits or systems in order to reduce the available fault current is not what 240.86 means when it gives approval for an engineered solution stamped by a PE.
I not say contrary in this:
Scenario
Equipment old-no listed series combination
Upstream impedance, no-space constraint

240.86(A) not avoid then
 