Sorry to get involved so late ....
110.10 requires that the component ratings for the component (contactor) be selected so there is no extensive damage to the component.
No document says that you can use the current let through ratings of a fuse to achieve the component ratings unless it has been tested (tested combination). This is clearly stated in the NEC for OCPD's and the intent IMHO is the same for the withstand of a component. At least I would not my company's name on the project unless it was a tested combination.
110.10 requires that the component ratings for the component (contactor) be selected so there is no extensive damage to the component.
No document says that you can use the current let through ratings of a fuse to achieve the component ratings unless it has been tested (tested combination). This is clearly stated in the NEC for OCPD's and the intent IMHO is the same for the withstand of a component. At least I would not my company's name on the project unless it was a tested combination.