Martin,
Please keep in mind that I am only now wrapping my head around this. I request that David or Ron tell me what I've missed
I agree with you on the following point: If a fault goes through both the fuse and the breaker, it doesn't matter which is 'closer' to the source. The two devices are in series on an AC circuit, and it will be a toss-up as to which opens first.
However a design distinction must be made between the downstream and the upstream device:
A downstream device is not considered to protect an upstream device; because a short circuit might bypass the downstream device.
If the fuse is downstream of the breaker, then the breaker would be _required_ need to be capable of opening the available fault current at the panel, just as if the fuse were simply not there, because the short circuit might be able to bypass the fuse. The downstream fuse can not be expected to protect the upstream breaker.
If the fuse is upstream of the breaker, and the breaker is _fully rated_ for the available fault current, then again there is absolutely no problem. Either the breaker or the fuse will open, but each will be within its rating, so no safety issue.
The issue of 'series ratings' and 'dynamic impedance' only comes into play if the downstream device is not rated for the available fault current. Now we are asking the upstream device to protect the downstream device. The up-over-down method is not a valid technique for determining if the upstream current limiting fuse will protect the downstream breaker. Only a properly tested 'series rating' will provide this information.
However if you have a properly rated circuit breaker protecting a branch circuit, and a fuse in the branch circuit to provide protection for 'static' downstream devices, then you don't have an issue of the fuse acting to protect the circuit breaker. Because of dynamic impedance it is not clear if the fuse or the breaker would trip first in a short circuit condition, but since the dynamic components (the fuse and the breaker) are both applied within their ratings, the dynamic impedance will not present as a safety flaw in the OCPD selection.
-Jon
Please keep in mind that I am only now wrapping my head around this. I request that David or Ron tell me what I've missed
I agree with you on the following point: If a fault goes through both the fuse and the breaker, it doesn't matter which is 'closer' to the source. The two devices are in series on an AC circuit, and it will be a toss-up as to which opens first.
However a design distinction must be made between the downstream and the upstream device:
A downstream device is not considered to protect an upstream device; because a short circuit might bypass the downstream device.
If the fuse is downstream of the breaker, then the breaker would be _required_ need to be capable of opening the available fault current at the panel, just as if the fuse were simply not there, because the short circuit might be able to bypass the fuse. The downstream fuse can not be expected to protect the upstream breaker.
If the fuse is upstream of the breaker, and the breaker is _fully rated_ for the available fault current, then again there is absolutely no problem. Either the breaker or the fuse will open, but each will be within its rating, so no safety issue.
The issue of 'series ratings' and 'dynamic impedance' only comes into play if the downstream device is not rated for the available fault current. Now we are asking the upstream device to protect the downstream device. The up-over-down method is not a valid technique for determining if the upstream current limiting fuse will protect the downstream breaker. Only a properly tested 'series rating' will provide this information.
However if you have a properly rated circuit breaker protecting a branch circuit, and a fuse in the branch circuit to provide protection for 'static' downstream devices, then you don't have an issue of the fuse acting to protect the circuit breaker. Because of dynamic impedance it is not clear if the fuse or the breaker would trip first in a short circuit condition, but since the dynamic components (the fuse and the breaker) are both applied within their ratings, the dynamic impedance will not present as a safety flaw in the OCPD selection.
-Jon