I need to specify a circuit breaker for the primary side of transformer - using bussmann fault calculator but not sure which values I should use
I need to specify a circuit breaker for the primary side of transformer - using bussmann fault calculator but not sure which values I should use
As a conservative measure, select a breaking capacity for 200 amp breaker equal to that of the second 800 amp breaker.I need to install 200 amp breaker for line side of 225kva xfmr on the load side of the second 800 amp breaker
I need to install 200 amp breaker for line side of 225kva xfmr on the load side of the second 800 amp breaker
Std impedance is going to be around 4.8%, for a 225KVA transformer with std tolerance of +/-7.5%. For Short circuit it's the -7.5% that is used.
Thus for 225KVA @ 4.46%; Max thru fault SC is roughly 5.045MVAsc. Using those numbers can get you in the ballpark for rating requirements at transformer.
I don't have the one line available so I don't know the size or impedance of the transformer to the MDP. From MPD 800 AMP 480 CB 100k rated travels about 140 ft to another 800 amp breaker 30k rated with parallel 500s. I need to install 200 amp breaker for line side of 225kva xfmr on the load side of the second 800 amp breaker
I may have misread but I think he is questioning devices on the line side
A 200A breaker seems awfully small for the primary of a 225kVA transformer.
It is by design; there is no secondary OCPD and I need to limit the secondary current
It is by design; there is no secondary OCPD and I need to limit the secondary current
I don't have the one line available so I don't know the size or impedance of the transformer to the MDP. From MPD 800 AMP 480 CB 100k rated travels about 140 ft to another 800 amp breaker 30k rated with parallel 500s. I need to install 200 amp breaker for line side of 225kva xfmr on the load side of the second 800 amp breaker
What's the secondary voltage and what is it supplying?
buffalony,
I just saw this explanation of the circuit and write to append my post.
Your 200-amp breaker should match the 30kA rating for the 800-amp panel main. That's the easy answer. If you're trying to reduce the rating to something less than 30kA, you could look to use NEC 240.86 Series Ratings and find a breaker that's listed with the model of the 800-amp, 30 kA rated breaker to get you to 30kA.
I need to specify a circuit breaker for the primary side of transformer - using bussmann fault calculator but not sure which values I should use
We are a plastics extrusion company; extruders have long barrels with resistance heaters attached. We use 480/240 delta-delta XFMR to supply single phase heaters. They installed parallel secondary conductors to distribution blocks to power the 3 and 4 kw heaters. They installed a 300 amp breaker on the primary. I am eliminating one of the secondary sets of conductors and so I need to limit the primary current to limit the current on the now single secondary conductors.
Without knowing all the details, it sounds like the conductors from the distribution blocks to the heaters is a violation of 240.21.
Also, will the 200A c/b properly protect the now single set of secondary conductors per 240.21(C)(1)?
... I need to limit the primary current to limit the current on the now single secondary conductors.