Why are you digging so deep on this topic…curious, direction from CBO ?
Why are you digging so deep on this topic…curious, direction from CBO ?
If you need real numbers, you need someone to run the system in one of the electrical engineering software programs...everything else is just a good guess.
hhsting
Why are you digging so deep on this topic…curious, direction from CBO ?
Chief Building Official…top dog.
So where that is required, you make the design engineer provide the required information, and unless you have very solid reasons to doubt what has been provide, you just use that information. If your permitting process does not require that type of information, you just comment on the plans that this may not be in compliance with the rules in the NEC.Take a look at NEC 110.9 and 110.10 and 240.86 first paragraph and part C. Thats why. You cant get that without short circuit w motor contribution.
Then why are you questioning it?
Designers often use simplified techniques and then specify a through study as part of the project contract.
So where that is required, you make the design engineer provide the required information, and unless you have very solid reasons to doubt what has been provide, you just use that information. If your permitting process does not require that type of information, you just comment on the plans that this may not be in compliance with the rules in the NEC.
Yes....study happens after approval of plans?
Yes.
The official study occurs after the project has been started.
It is very common to have the short circuit study identify design short comings resulting in changes to equipment that has already been approved, order, and sometimes installed. The AHJ looks at the study as part of their final approval.
I really don't know.Exactly who in AHJ looks at the study as part of final approval reviewers, inspectors who?
Lots of things in a permitting process are not found in the NEC such as a requirement to provide a fault current study as part of the permit application.What?! Permitting process require to follow NEC 2017. Yea solid reason is it can be way off, loose estimate
Lots of things in a permitting process are not found in the NEC such as a requirement to provide a fault current study as part of the permit application.
In many cases, they cannot be complete until after the project has been installed as the actual conductor lengths makes a difference in the fault current. At the design stage, the designer would typically use a conservative estimate and that is all you really need for plan review.
You just use what has been provided and require changes after the fact if there is an issue after completion.
I would just note on the plans, that they are approved pending the final, after installation, short circuit study, and that if the equipment is not in compliance at that time, it will have to be replaced. This will give enough push to the owner, designer, and installer to be sure that the original installation is compliant.
While those sections do require the calculations, nothing in those sections requires the calculation be made available to the inspection authority as part of the permit process.110.9 and 110.10, 240.86(c) first paragraph all of them NEC 2017 version require fault current calculations. I am not sure where you are getting its not in NEC?
While those sections do require the calculations, nothing in those sections requires the calculation be made available to the inspection authority as part of the permit process.
You are asking for information that the NEC does not require the engineer to provide. There are some rules where the code requires calculations to be made available to the AHJ, those sections do not.
If you want that information to be provided with the plans submitted for plan review, your local permit ordinance must specify that the short circuit study be supplied along with the plans and specifications when they are submitted for review.
Which sections require calculation?
Also I still dont follow how you can say those section dont require fault current calculation. Interrupt rating must be greater than available fault current. If they dont provide interrupt rating at all and they dont provide fault current calculation then how do I know if NEC 2017 section 110.9 or 110.10 comply? I cannot do that without fault current calculation that is saying short circuit fault current calculation
NEC 2017 section 240.86 first paragraph in order to verify if it applies say available fault current must be greater than interrupt rating. NEC 2017 section 240.86(C) says higher rated device and lower rated deci e how do I know if all that applies if fault current calculations and interrupt rating not provided?
Remember this is a high rise and also this is brand new building.
You are not reading what I am saying. I have never said that the calculations are not required.Which sections require calculation?
Also I still dont follow how you can say those section dont require fault current calculation. Interrupt rating must be greater than available fault current. If they dont provide interrupt rating at all and they dont provide fault current calculation then how do I know if NEC 2017 section 110.9 or 110.10 comply? I cannot do that without fault current calculation that is saying short circuit fault current calculation
NEC 2017 section 240.86 first paragraph in order to verify if it applies say available fault current must be greater than interrupt rating. NEC 2017 section 240.86(C) says higher rated device and lower rated deci e how do I know if all that applies if fault current calculations and interrupt rating not provided?
Remember this is a high rise and also this is brand new building.
You are not reading what I am saying. I have never said that the calculations are not required.
All I am saying is that the NEC does not require those calculation to be provided to you as part of the permit process. If you want those to be provided, your local ordinance that covers permit applications must specifically require that the person or company requesting the permit provide you with those calculations.
Sections 110.9 or 110.10 do not require "calculations", they simply require that equipment/devices are properly applied. Calculations are one method to demonstrate compliance. Based on this thread (in addition to what I already explained to you in the DM), I believe your questions have been thoroughly answered. Whether you agree or want to accept it is another issue altogether.Well if AHJ building plan review has adopted NEC so this means as part of permit process AHJ is to check the plans against whats in NEC to see if plans comply or not and NEC requires calculation then how do you say NEC does not require those calculation to be provided as part of permit process?
I apologize but I am having hard time understanding. I really appreciate your help and patience