To me it would make much more sense to provide fault current study with plan conservative one for complex projects like high rise, hospitals and be done with computer software with PE sign and seal no hand written calcs so that reviewers can verify that what is installed comply with installation rules provided in 110.9 and 110.10
So all of you are saying fault current study is required for sure to verify the install comply per NEC 2017 section 110.9 and 110.10 but NEC 2017 section 110.9 and 110.10 does not state that fault current study be provided with plans, or if not with plans then to inspecting authority meaning to inspectors if not to reviewers
In our department permitting agency their is no rule provided to submit fault current calculation study with plans, which method to use nor their is rule to provide fault current study to inspectors.
In our department permitting agency Inspectors do Not verify AIC ratings downstream of main service equipment. Of course main service equipment Available fault currents are verified because I am guessing NEC 2017 section 110.24(A)
This creates problems. Now problems:
a. lets say fault current study is done then our inspecting authority would not verify it downstream of main service equipment. Reviewers cannot ask for it during review time.
So then who is responsible if something goes wrong checking if fault current study is provided and how is 110.10 and 110.9 rules be enforced or checked?
b. Lets say fault current study is Not done reviewers cannot ask for the study during review time. Whose to see if the required fault current study is done? So then who is responsible if something goes wrong checking if fault current study is provided and how is 110.10 and 110.9 rules be enforced or checked?
c. Is their Anywhere in NEC 2017 that requires fault current study be provided to AHJ, reviewers, inspectors, inspecting authority, to verify the installation rules of 110.10 and 110.9 are complied?
First, the Engineer of Record is responsible for his design and owns the liability for any errors/omissions in his/her work. It’s their legal duty to ensure that all elements of the submittal to the building official or public authority are compatible, coordinated and provide a logical and comprehensive document.
Second, the building official is charged with the administration and enforcement of building codes. Note: you are not the building official, you are authorized staff directed to enforce provisions of “adopted codes and ordinances” by regulating and controlling the design, construction, use, location, energy conservation, and maintenance of all buildings, structures and other improvements within the jurisdiction.
Third, Let’s not forget, “This Code is not intended as a design specification or an instruction manual for untrained persons.”
At the end of the day, if there was an accident because of overdutied equipment (resulting form a design error), the Engineer of Record would be implicated. His lawyer could always argue at the time of plan submission, no such administrative procedure existed to perform a fault study, and the plan reviewer even approved the plans.
If you demand additional information without having a code/ordinance to fall back on, and then approve the plans once documentation is provided, your liability in the matter has just increased and your qualifications to evaluate such information could be called into question (several liability).
If you reject plans, you must have references to codes/ordinances and provide sound technical facts as to where the deficiency lies. If they are not legitimate or legal reasons for rejecting a design, expect to get pushback.
Also, not sure why some of you think short-circuit “calculations” are required in the NEC. There is no such language.