I see no issue with you rejecting the plans based on incomplete information and requiring a revised set of plans that show the required SSCR and AIC ratings.
But even that could be an issue where the administrative rules do not require the submission of plans with the permit application.
Well yea we have admin rule to submit plans alright PE stamp sign and seal with permit application but don’t see no admin rule saying to provide SSCR and AIC rating. Admin rule says electrical plans comply with NEC 2017 and local chapter 17 which does not have no rule to submit SSCR and AIC rating.
So thats the problem how does one solve this if they don’t provide AIC rating at all and no SSCR panel schedules, meter stacks schedule?
It has to be approved conditionally with note all AIC ratings comply with short circuit study with motor contribution?