Having read through the thread again, I'm tending to agree with the open-neutral theory. It sounds like the POCO is looking to pass the blame onto one of its customers; in this case, yours.Question remains can the fault in one home be transmitted out onto the grid and affect other homes fed by the same pole mounted transformer in this situation?
Imagine a pond of water that is perfectly calm. You throw a rock about the size of a tennis ball in the center of the pond, creating waves.
I'm quite sure the disturbances in my home are not affecting yours in any way shape or form.We call this the "ripple effect". When you cause disturbances within your home, the rest of the power grid will feel it. Usually this shows up as unstable voltage, or a disturbance in harmonics (harmonic distortion). Imagine a pond of water that is perfectly calm. You throw a rock about the size of a tennis ball in the center of the pond, creating waves. This represents fundamental current, fundamental waveform. Now throw another rock 1/3 the size in the pond off to the right of center, creating another set of waves. Now you have created harmonic distortion, away from the original fundamental waveform. If you could measure the difference between the first waveform, and the second, you would be calculating THD, or "total harmonic distortion".
Similar to the butterfly flapping it's wings in Brazil affecting our weather here.It’s subtle, but they do.
For Want of a NailThere is a Dutch children's book that starts with a nail entering a horse's hoof, the nail not removed, that leads to the complete collapse of a nation by war, starvation.
For want of a nail the shoe was lost.
For want of a shoe the horse was lost.
For want of a horse the rider was lost.
For want of a rider the message was lost.
For want of a message the battle was lost.
For want of a battle the kingdom was lost.
And all for the want of a horseshoe nail.
I felt bad for my part in this so I just now votedThis is par. We all have opinions but only two have voted.
In theory, which is a large caveat, a bolted fault between one line conductor and the neutral could pull the neutral far enough away from its nominal voltage that devices driven between the other phase and neutral could see a damaging overvoltage condition.Ok well thank you everyone for that information. This is a great platform. When I said a “fault “ that was a very broad term. So that could cover just about everything.
So we know that the 220v / 240 v whatever the case may be is derived from the pole mounted transformer and we are not talking about a fault there. So correct me if I’m wrong but the voltage from the residence can never be more than it was supplied. That means we are talking about a fault current . In order to trip the network protection device on the primary side of the transformer the current would have to be extremely high. Agreed?
The service into the house looks unscathed. Main CB not tripped. Fire on the opposite side of the house from the service drop. So that means the fault was within a branch circuit. I’ll give you the benefit of doubt and say the fault occurred at an electric range on a 220v 50A CB. Question is - is that fault current enough to cause an issue at the neighbors house in anyway?
At the customer's end of the service drop/lateral, and for a short (no pun intended) time, yes.In theory, which is a large caveat, a bolted fault between one line conductor and the neutral could pull the neutral far enough away from its nominal voltage that devices driven between the other phase and neutral could see a damaging overvoltage condition.
Not without a defect of some kind (*cough* bad neutral *cough*) ahead of the dividing point.However, I think it should not be possible for that overvoltage condition to reach a customer served by a separate service drop from the POCO secondary winding.
It would require several extraordinary conditions to exist simultaneously for an occurrence to extend from one service into a separate service off the same xfer. As some suggested most likely would have to carry from something on the neutral.Can an electrical fault in a residence be transferred out onto the service grid affecting other homes in the area on the same secondary side of the transformer?