Federal pacific breakers

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
I know that federal pacific had a problem with stab lock breakers. are the bigger molded case breakers safe ( non stab lock ) ?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I know that federal pacific had a problem with stab lock breakers. are the bigger molded case breakers safe ( non stab lock ) ?


I don't believe those breakers where the issue. I believe it had to do with many DP 30 amp breakers and perhaps some others
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Check this out

[FONT=&quot]The Commission investigation into Federal Pacific Electric (FPE) circuit breakers began in June 1980, when Reliance Electric Co., a subsidiary of Exxon Corporation and the parent to FPE, reported to the Commission that many FPE circuit breakers did not fully comply with Underwriters Laboratories, Inc. (UL) requirements. Commission testing confirmed that these breakers fail certain UL calibration test requirements. The Commission investigation focused primarily on 2 pole residential circuit breakers manufactured before Reliance acquired FPE in 1979.[/FONT]
[FONT=&quot]To meet UL standards residential circuit breakers must pass a number of so-called "calibration tests." The purpose of these tests is to determine whether the circuit breakers will hold the current for which they are rated and also automatically open or "trip" (shut off the current) within specified time limits if overloading of the circuit causes current levels in excess of the breaker's amperage rating. (Overloading can occur because a consumer plugs too many products into a circuit or due to the failure of a product or component connected to that circuit). While the Commission is concerned about the failure of these FPE breakers to meet UL calibration requirements, the Commission is unable at this time to link these failures to the development of a hazardous situation.[/FONT]
[FONT=&quot]According to Reliance, failures of these FPE breakers to comply with certain UL calibration requirements do not create a hazard in the household environment. It is Reliance's position that FPE breakers will trip reliably at most overload levels unless the breakers have been operated in a repetitive, abusive manner that should not occur during residential use. Reliance maintains that at those few overload levels where FPE breakers may fail to trip under realistic use conditions, currents will be too low to generate hazardous temperatures in household wiring. Reliance believes its position in this regard is supported by test data that it provided to the Commission.[/FONT]
[FONT=&quot]The Commission staff believes that it currently has insufficient data to accept or refute Reliance's position.[/FONT]
[FONT=&quot]The Commission staff estimates that it would cost several million dollars to gather the data necessary to assess fully whether those circuit breakers that are installed in homes but which may fail UL calibration tests present a risk to the public. Based on the Commission's limited budget ($34 million for fiscal year 1983), the known hazards the Commission has identified and must address (involving products of other manufacturers) and the uncertainty of the results of such a costly investigation, the Commission has decided not to commit further resources to its investigation of FPE's circuit breakers. However, despite its decision to close this particular investigation, the Commission will continue its investigation of circuit breakers generally. The Commission can reopen its investigation of FPE circuit breakers if further information warrants.[/FONT]
[FONT=&quot]The Commission advises consumers to take certain safety precautions with all circuit breakers and fuses. Consumers should:[/FONT]
[FONT=&quot]- Know your electrical circuit. Know which outlets and products are connected to each circuit.

[/FONT]

[FONT=&quot]- Never overload any electrical circuit by connecting too many products to the circuit. Be particularly careful not to connect several products that demand high current (such as heating appliances) to a low amperage circuit.

[/FONT]

[FONT=&quot]- Comply with local building codes in wiring or adding electrical circuits. Make sure the wiring and devices used in the circuit are connected to a circuit breaker or fuse of the proper size.

[/FONT]

[FONT=&quot]- Immediately disconnect any electrical product if problems develop. Have the product examined by a competent repair person.

[/FONT]

[FONT=&quot]- Investigate to determine why a fuse blows or circuit breaker trips. Do not simply replace the fuse or reset the breaker. If a fuse blows or breaker trips, it is often a warning that the circuit is overloaded. Check the circuit for causes of overloading (for example, too many appliances plugged in, a malfunctioning product, a short circuit). When in doubt, consult a licensed electrician.[/FONT]
[FONT=&quot]Consumers who have questions concerning circuit breakers, or who wish to report information relating to their safety, may call the U.S. Consumer Product Safety Commission's toll-free safety hotline at 800-638-CPSC.[/FONT]
 

JFletcher

Senior Member
Location
Williamsburg, VA
I don't believe those breakers where the issue. I believe it had to do with many DP 30 amp breakers and perhaps some others

The double pole (not just 30A) stab-loc were the problem, apparently with the way the common trip mechanism worked, and with reset. Parts got bent/jammed and the breaker would never trip again, giving all the names to FPE gear like "welding panels". ofc that's ignoring the other design flaws, like tiny bus contacts and needing a properly adjusted deadfront to hold the breakers in. and that most FPE gear is 60+ years old.

afaik their single pole stab loc breakers didnt have the 2p problem, nor did any of their larger gear. That said, if I ever run across a tripped 2p stab loc breaker, it's going in the trash.
 

JFletcher

Senior Member
Location
Williamsburg, VA
That is why I said and perhaps some others and then posted the link



Why? Those are the ones that work....:lol: The problem was they weren't tripping

:D

The problem with the 2p is that if one pole of the two tripped, it would trip the whole breaker, but damage itself (jam, I believe) internally, so that if/when reset, it would never trip again (because the guts are jammed) Thus any 2p FPE stab lock I find tripped is going in the trash. I can find a link on the problem later.

I did a fair amount of research on FPE panels a few years ago because this house had one of the Federal No-Ark (stab loc) boxes in it.
 