Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
So to my prior question in my first post I guess I don't need to know the calculated load for the panel the wire is feeding? I would only size the feeder off of the breaker upstream that is protecting the conductors irregardless the panel size it's feeding? So above in first post an 800a breaker is feeding panel. I'd size wire off 800a.the conductors are protected by the upstream 400a breaker. So it needs 400a conductors. 500kcmil would work. The DEMAND LOAD is only 77a. So if the upstream breaker could be reduced to 100, you could use 100a conductors.