A 460V 60HP bakery mixer fed through a 240X480 112.5KVA transformer. This transformer is fed from a 2400X240 150KVA substation. The mixer does not operate properly.
However When the primary is disconnected and the 240V side is fed from a 300KVA generator, it does operate properly.

Any immediate thoughts on reasons why the utility feed is not working?
The owner thinks it may be a too-small primary feeder to the substation. (size unknown)
Could grounding have anything to do with it?
 
Grounding probably has nothing to do with this problem. Someone needs to measure the voltage going to the mixer from the transformer and see if it is correct.

Also what does it mean when you say it does not operate properly?
 
Suggest following tests
Open ckt voltage, running voltage, inrush amps, running amps, on existing xfmr and generator.
 
Thanks. All good questions.
No one thinks, assuming everything is hooked up correctly, that there should be an issue?
 
Should not make a difference but we still don't know what "doesn't operate properly" means so it s more a shot in the dark.
Sight unseen, my money would be with Jons' idea: rotation !
 