I am currently bidding a job where the engineer has designed a generator connection cabinet that will feed (3) services in the event of an extended outage. The cabinet will be rated at 2500 A and will feed the (3) services through Kirk-keyed breakers in the MSB's. The problem is, they show the output of the connection cabinet running to a "junction box" as they call it, and then branching out to the services. Each feeder will have (7) sets of (3) 700 kCMIL for a total of (28) conductors per phase including the incoming (and the grounded conductors).
What would be group's thought on what to use as the "junction box" ? I checked CMC utility products and their cabinets accept a maximum of (14) per phase. I'm thinking maybe some sort of bussed manhole ?
I've not come up against anything like this in nearly 45 years, so I'm open to suggestions. Thanks