The one on the right doesn't comply with the tap rules.
5-500 kcmil=200% neutral, not uncommon if 3Ø. Is it 3Ø?
275 amp fuse? That not a standard NEC size.
According to the way that it's drawn there are two separate feeders. Since the 400 amp OCPD at the top right is full size there is no tap.
Then why a 1/0 equipment grounding conductor
5-500 kcmil=200% neutral, not uncommon if 3Ø. Is it 3Ø?
275 amp fuse? That not a standard NEC size.