5-500 kcmil=200% neutral, not uncommon if 3Ø. Is it 3Ø?

275 amp fuse? That not a standard NEC size.
 
5-500 kcmil=200% neutral, not uncommon if 3Ø. Is it 3Ø?

275 amp fuse? That not a standard NEC size.


I wonder if the ee doesn't realize that at 380 amps 400 amps overcurrent protective device is compliant. I don't understand the 1/0 equipment grounding conductor. I am wonder if he is using 800 for the 2- 400 amp wires -- I hope he is not considering this a parallel install and using an 800 amp overcurrent protective device... that would be 1/0

Or... maybe that jumper in the splice box is tying them together-- got it
 
According to the way that it's drawn there are two separate feeders. Since the 400 amp OCPD at the top right is full size there is no tap.
 