MyCleveland
- Cleveland, Ohio
Anywhere NEC text = "Feeder", can you replace with "Tap Feeder" as an equivalent statement ?
In what way? While the supply conductors are taps, they are by themselves still technically a feeder per the Article 100 definition.Design: Multi-Family
208Y/120 distribution - Apartments are 120/208V-1P-3W
Riser 4W feeder from distribution panel...vertically or horizontal to serve 3, 4, 5 and even 6 apartments.
Each apartment served via 3W "Tap Feeder" connected to riser.
Apartment load sized via 220.82
Is this not a violation of 220.82(A)
Again, in what way? 220.84(A)(1) states each dwelling unit is supplied by no more than one feeder. According to your description, only one feeder (or one feeder tap) supplies power to each unit.Riser load sized via table 220.84
Is this not a violation of 220.84(1)
How many sets utilize a common neutral? You made no mention of the feeders having a common neutral. 208Y/120 being a 4 wire system, you can run two feeder sets with one common neutral (7 circuit conductors total).Tap Feeders serving 4, 5, and 6
Is this not a violation of 215.4(A)
Supply conductors to apartment, "Tap Feeder" is then the same as "Feeder"Welcome to the forum... :thumbsup:
What I am describing is a 4W riser serving 3-6 3W Taps, ALL of which SHARE the 4W riser NEUTRAL, does this not violate 215.4(A)My opinion...from the information given...
No.
Does not a Tap Feeder (3W), connected to a 4W riser result in apartment served via TWO feeders
No.
Same for 220.84A)((1), apartment is serviced via two feeders, and therefore access to derating table 220.84 is not allowed
Not per se. If you're concern is that the riser neutral supplies multiple taps, that is not a violation.
All 3W Tap Feeders are connected to the 4W riser, therefore you end up with 3-6 3W Tap Feeders SHARING a common neutral....215.4(A) states this is not allowed.
What you are describing is one feeder that supplies multiple other feeders through taps. The main feeder must be sized for the total load of all units. Each feeder supplied by a tap must be sized for the dwelling unit it supplies. The tap rules must be followed to make this a compliant install. But I don't see anything that you've described as a violation in and of itself.
I get what you are saying, but I dont see it that way. IMO the feeder taps end where they connect to the single feeder (riser) which is just 1 feeder. I dont see the feeder taps (which as pointed out by smart$ are a type of feeder) as sharing a neutral.
100A apartment load example could result in a common riser beingsized SMALLER than the TAPS serving each apartment.
Three apartments of 20.8kW load, which equates to exactly a 100A – 120/208V-1P-3WTAP feeder serving each apartment.
20.8 x 3 = 62.4kW
Access to derating table 220.84
62.4 x 0.45 = 28.1kW
Total load for sizing riser = 28.1kW
Riser ampacity = 28,100/(208)(1.73) = 78.1 amps
Result is I can serve THREE 100A single phase apartments with an 80A (PHASE& NEUTRAL conductors) 4W common riser feeder.
No. The feeder tap is a feeder in and of itself. What differs is that its protection is at the load end rather than the source end. Only this last feeder is the one that counts whether the dwelling unit is served by more than one feeder. Think of it like this... would it be two feeders if the protection (breaker, fuses) was where it taps the riser feeder?Supply conductors to apartment, "Tap Feeder" is then the same as "Feeder"
Again, no. You'd have to have a seven wire riser, i.e. 2 feeder sets of ungrounded conductor to share a common neutral: A1, A2, B1, B2, C1, C2, N.All 3W Tap Feeders are connected to the 4W riser, therefore you end up with 3-6 3W Tap Feeders SHARING a common neutral....215.4(A) states this is not allowed.
No, I don't believe that's what 215.4 refers to. If each of the tapped off feeders has a neutral tapped with it, then those are the neutrals for those feeders, and none are shared. The 'riser' is a separate feeder and its neutral only belongs to the riser.
Taps off the feeder neutral conductor are not counted as sharing the neutral for this requirement.
The way I see it, you have a good mind set. But you are lacking in your Code training. As stated in 90.1 "This Code is not intended as a design specification or an instruction manual for untrained persons."
untrained persons - first day on the site, should I sign off ?
There is no common neutral shared with multiple circuits. You have one neutral for the feeder circuit and a neutral with each tap circuit. None are common to more than one circuit. The feeder circuit does not extend into the tap circuits. A new tap circuit neutral starts at the point of connection to the feeder circuit neutral.Your (A1, A2, B1, B2, C1, C2, N) scenario describes exactly a 3 apartment riser with taps connected to the 4W riser and ALL sharing a common N.
There are no common neutrals in this application. You have one feeder circuit with a neutral. You have multiple tap circuits each with their own neutral.
I see your point with the math...simply change the apartments to standard calc design at 20.6kW each.
I think you're missing something there.
220.82 allows a calculation based on 100% of the first 10kVA plus 40 percent of the remainder. If that number is 20.8kVA (requiring a 100A feeder), then your total summation of considered loads was 37kVA to start with.
220.84 applies to the total considered load without any allowance like the one in 220.82. Thus if you had 3 units requiring a 100A feeder you'd have 37kVA*3=111kVA. Apply 45% to that and you get 50kVA, which when you divide by 208V and 1.73 requires a 138A feeder.
Note: None of this has anything to do with whether you have a feeder that gets tapped, or taps vs feeders. You could have a service with a main breaker and three feeder breakers to dwelling units; no taps, but the calculations would be the same.
Also note: if the main feeder (riser) ungrounded conductors are protected properly at their ampacity then as long as the neutral is sized the same it cannot see an unbalanced current that's greater than its ampacity. The fact that the downstream feeders might be 3W instead of 4W is quite irrelevant to that.