I am getting into this one late, and I need to digest the discussion before offering an opinion. But I will start with this:
Nowhere in the discussion did I see evidence that there are any "taps" involved in the installation at all. Specifically, I have not seen mention of wire sizes or ampacities. To directly answer this question, no they are not the same. You don't have a "tap" unless, (1) You connect wire 2 to wire 1, (2) The OCPD protecting wire 1 is rated higher than would normally be needed to protect wire 2, and (3) You don't install an OCPD at the point of connection of wire 2 to wire 1, so that that OCPD protects wire 2 at its ampacity. I think we have item (1) in this installation, but we don't yet know about items (2) or (3).Anywhere NEC text = "Feeder", can you replace with "Tap Feeder" as an equivalent statement ?