Numerous pieces of equipment are being moved out of a building's mechanical room to another small shell structure right outside the building to make room for additional equipment. We hoped to just extend existing circuits for all these mechanical equipment to the shell structure. I thought that some disconnects on the outside of the shell structure would suffice to meet NEC requirements.
However, it seems that Article 225.30 limits the number of supplies to a building to just one feeder. There are some exceptions listed including the rather vague "Documented Switching Procedures" one, but either way 225.31 still requires there to be a single disconnecting means to turn off all power to all feeders.
The single disconnecting means requirement listed in 225.31 is achievable with some relays and contacts, but can we supply a shell building with multiple feeder circuits? I would think yes....
However, it seems that Article 225.30 limits the number of supplies to a building to just one feeder. There are some exceptions listed including the rather vague "Documented Switching Procedures" one, but either way 225.31 still requires there to be a single disconnecting means to turn off all power to all feeders.
The single disconnecting means requirement listed in 225.31 is achievable with some relays and contacts, but can we supply a shell building with multiple feeder circuits? I would think yes....