The question is can feeders run through  privately owned attached single family dwellings that are seperated by  zero lot lines at the fire walls build over the seperating basement  concrete foundation walls. These are not condominiums, each structure  has a property line that runs fron the street, straight through the  center of a double framed partioning wall. They want to mount the  meter/disconnects at one end and run SER through the joist of each owned  dwelling penetrating the fire wall sepertion in the first floor joist. I  am saying they can't unless run below the slabs in conduit and their  point of entry will be where they come up into each individual unit, I  also believe they can then not include the exterior disconnect as long  as the point of entry is within a reasonable distance to the MDP. If I  am correct these will not be called feeders any longer but service  enterance cables.
Any code section would help!
		
		
	 
Yes you can do that.
Also you what to check with your local building code.
Welcome to the forum..:thumbsup:
300.21 Spread of Fire or Products of Combustion. Electrical
installations in hollow spaces, vertical shafts, and
ventilation or air-handling ducts shall be made so that the
possible spread of fire or products of combustion will not
be substantially increased. Openings around electrical penetrations
into or through fire-resistant-rated walls, partition
floors, or ceilings shall be firestopped using approved
methods to maintain the fire resistance rating.
Informational Note: Directories of electrical construction
materials published by qualified testing laboratories contain
many listing installation restrictions necessary to maintain
the fire-resistive rating of assemblies where penetrations or
openings are made. 
Building codes also contain restrictions
on membrane penetrations on opposite sides of a fireresistance-
rated wall assembly. An example is the 600-mm
(24-in.) minimum horizontal separation that usually applies
between boxes installed on opposite sides of the wall. Assistance
in complying with 300.21 can be found in building
codes, fire resistance directories, and product listings.