In a 208V 3-phase building I am feeding chiller module. The available fault current at the service is 128,000 amps.
The chiller module has these specs:
LRA: 1359 amps
MCA: 930 amps
MOP: 986 amps
Recommended fuse size: 800 amps
The short circuit rating of the chiller module control panel is 10,000 amps. The chiller module will be 120 feet away from the power source.
How the heck do I get 10,000 amps from 128,000 amps? The length of the run would be astronomical with terrible voltage drop.
If I need a line reactor, which one do I get? Wouldn't the line reactor be extremely large? I'm also worried about the voltage drop too if the line reactor is installed. I am not even sure if this installation is feasible..
LRA: 1359 amps
MCA: 930 amps
MOP: 986 amps