synchro
Senior Member
- Location
- Chicago, IL
- Occupation
- EE
If you did use a transformer to increase the source impedance, you'd be better off having it boost the voltage up to 480V since the chiller manufacturer has a version for 460V and it still has the same 10 kA SCCR as for 208V.
If you broke it up into two 4 stack modules and had a 225 kVA 208/480V transformer for each one, the online calculator below gives a ~9 kA short circuit current with 3% transformer impedance and ~5.5 kA with a 5% impedance. This apparently assumes a zero source impedance, and also no impedance from circuit conductors has been included. I haven't tried to determine how accurate this calculator is, but I'm assuming it's at least in the ballpark.
I agree with the others that if you can get the manufacturer to supply an SCCR of 65 kA that would be best.
https://voltage-disturbance.com/power-engineering/power-engineering-impedance-of-transfromer/
If you broke it up into two 4 stack modules and had a 225 kVA 208/480V transformer for each one, the online calculator below gives a ~9 kA short circuit current with 3% transformer impedance and ~5.5 kA with a 5% impedance. This apparently assumes a zero source impedance, and also no impedance from circuit conductors has been included. I haven't tried to determine how accurate this calculator is, but I'm assuming it's at least in the ballpark.
I agree with the others that if you can get the manufacturer to supply an SCCR of 65 kA that would be best.
https://voltage-disturbance.com/power-engineering/power-engineering-impedance-of-transfromer/