Feeding Chiller Module

topgone

Senior Member
The unit already has a built in disconnect so I don't know what the heck they're talking about in that manual. See below circle in blue

View attachment 2571155
OSHA requires a separate switch to isolate power when servicing that equipment. If that disconnect switch is located away from view and not lockable, tinkering on equipment that's not isolated could result in electrocutions. Your attached picture allows some wires entering the cabinet/s energized even if you put the cabinet CB off. it's not the safety of the installer, AHJ is looking at possible scenarios beyond the point of installation.
 

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
OSHA requires a separate switch to isolate power when servicing that equipment. If that disconnect switch is located away from view and not lockable, tinkering on equipment that's not isolated could result in electrocutions. Your attached picture allows some wires entering the cabinet/s energized even if you put the cabinet CB off. it's not the safety of the installer, AHJ is looking at possible scenarios beyond the point of installation.
well in this case , my disconnect switch will be far away and lockable
 