That begs another question: does your heat in the shaft activate the shunt? We have it to recall away from the detector, which makes more sense to me. Shunting on the shaft detector would essentially be locking passengers in with the fire.
Our programmer had it that way, it was changed to alternate recall on heat in the shaft.
Oh you disagree with the idea of being trapped in a metal box with a fire below you???????
Yea, its in ANSI A17 I believe.
What first is supposed to happen is the smoke at the top of the shaft, performs a recall to the main floor and you cannot move the elevator, unless you place it in phase II operation (firefighter key control).
Then
If the heat trips the panel, the panel trips a relay to activate the shunt.
The theory is, the heat detector trip temp(135F) is lower than the sprinkler head (165F) The sprinkler head and heat have to be within 2' of each other in the pit. So the heat will trip the shunt, kill the power, so when (if) the sprinkler head pops it will put out the fire and you wont mix water and electricity.
Realistically speaking the sprinkler head at the top of the shaft will go first, and you are getting wet anyway.
I agree with the delay timer option, but that's not how everyone does it. In MA, nothing in the pit (they have changed their minds about that, 5 years ago we had to pull out every smoke in every elevator pit, in a few more years we'll probably put them back)
In NH a heat is required, when sprinklered.