Good day all,
I am doing the electrical design for a small 8800 square foot clinic w/ a business occupancy. I do not believe I am required to provide a Fire alarm system, the building is sprinklered. Less then 500 occupant load.
The sprinkler system will require a tamper and flow switch and the building has one Roof top unit for HVAC that is over 2000 cfm and will require a duct smoke detector.
So?where do I connect these 3 fire alarm devices with no fire alarm system/panel?
Thanks you.
hoyt