thecrazyezel
All,
Having a real hard time here trying to figure out how to size the generator for the fire pump. We are in a high-rise, have a 120 HP fire pump, and we need to have this fire pump on the emergency generator. We know about limiting the voltage drop to 15% when starting under locked rotor conditions. We also know that the fire pump has to be able to start with all of the other emergency loads running simultaneously. Last but not least, we know that in case the soft starter fails that this fire pump can be started in manual mode but when it does, it starts across the line.
I plug in the other emergency loads and have a 230 kW generator with a soft starter on the fire pump. I change the fire pump to across the line and I get a whopping 500 kW genset. So here is the pickle I am in...I have to tell the Owner now that he has to more than double his generator size in case the normal power is out, there is a fire in your building AND your soft starter fails and we have to start the fire pump manually. This single requirement is driving all of this. Where does it say/stipulate this in the code - how do I get around it - or am I just stuck. Any help here would be greatly appreciated. If you could cite code that I could go back to the AHJs with that would be even better.