VENgineer
Member
- Location
- Miramar Fl
- Occupation
- Electrical Engineer
I have the following situation. A customer made a mistake in the purchase of a fire pump. The service voltage is 240V, and the fire pump operates at 208V (200V/400V) according to the nameplate.
As a result, when they attempted to start it, the controller triggered an alarm. My suggestion was to replace the fire pump, but the customer wants to install a transformer because, according to them, replacing the pump would take too long.
Therefore, the proposed solution is to install a 150kVA transformer , 240V - 208/120V. On the primary side, a 2000A breaker will be installed to comply with the NEC (National Electrical Code) fire pump requirements, considering a Locked Rotor Current(LRC) of approximately 1800A.
The fire department visited the site and stated that the transformer cannot be installed in the fire pump room. Consequently, it will be installed outside.
My question concerns the 2000Amp breaker.
(Fire Pump + Jockey Pump 125HP)
I appreciate any guidance on this matter. Thank you.
As a result, when they attempted to start it, the controller triggered an alarm. My suggestion was to replace the fire pump, but the customer wants to install a transformer because, according to them, replacing the pump would take too long.
Therefore, the proposed solution is to install a 150kVA transformer , 240V - 208/120V. On the primary side, a 2000A breaker will be installed to comply with the NEC (National Electrical Code) fire pump requirements, considering a Locked Rotor Current(LRC) of approximately 1800A.
The fire department visited the site and stated that the transformer cannot be installed in the fire pump room. Consequently, it will be installed outside.
My question concerns the 2000Amp breaker.
- Should it be installed in the fire pump room?
- Can it be installed outside next to the transformer, with its respective NEMA 3R enclosure?
- Or should it be installed in the main electrical room (I understand that the code requires it to be sufficiently remote from other disconnects for other loads; correct me if I'm wrong)? Therefore, I am ruling out this option.
(Fire Pump + Jockey Pump 125HP)
I appreciate any guidance on this matter. Thank you.