Thanks Jim
Based on your comments last sentence, assuming the rotor does NOT break free and the table from "augie47" about tranny overload, is it then a race between the motor and tranny destruction to see which clears the circuit first ?
That's the way I see it. Bring your own popcorn.
 
Thanks Jim
Based on your comments last sentence, assuming the rotor does NOT break free and the table from "augie47" about tranny overload, is it then a race between the motor and tranny destruction to see which clears the circuit first ?
Kind of.
After the motor windings begin to fail it is likely that a short circuit occurs somewhere. A fire pump supply OCPD is not required to carry any short circuit at all.
 