steve holt
Member
- Location
- Hawaii
If the fire pump controller is listed for use as a service disconnect, does the OCP needs to be based on Locked Rotor Current? The OCP in all controllers that I have seen, are sized based on FLA, not Locked Rotor.
Does that mean if it is listed, the breaker is supposed to be sized based on LR?If it’s a listed assembly, that sizing is all part of the listing. For fire pump service disconnect controllers, the is no OCP, just short circuit and ground fault.
The concept is sacrifice the motor in the event of a fire
If the fire pump controller is listed for use as a service disconnect, does the OCP needs to be based on Locked Rotor Current? The OCP in all controllers that I have seen, are sized based on FLA, not Locked Rotor.
Does that mean if it is listed, the breaker is supposed to be sized based on LR?
Which is what I said in post #2Inside fire pump controller listed device breaker is sized and set by the manufacturer you dont touch. If you want to know where it set at contact your manufacturer if it complies per nfpa 20 then see previous thread. But still you dont touch
Which is what I said in post #2
I don’t know, I have only installed 2 fire pump controllers and they were sized by HP, voltage snd phase
The first one was in 1999 and the second in 2010. I didn't provide the lugs. Incoming was about 3/0 CUSince you installed 2 fire pump controllers Tom do you know what size equipment grounding conductor lug and incoming phase conductors where? Did the EGC lug came with manufacturer fire pump controller or you provided them?
Sent from my iPhone using Tapatalk
Thats a sneaky way to get a question answered from another postSince you installed 2 fire pump controllers Tom do you know what size equipment grounding conductor lug and incoming phase conductors where? Did the EGC lug came with manufacturer fire pump controller or you provided them?
Sent from my iPhone using Tapatalk
You can look it up on the suppliers web site based on the type of controller.
I'll be nice and show you pic from an Eaton pdf
Here is a good read for you. Directly related to your question.
Your welcome.CQD: 11/28/2014
www.neca-neis.org
The way I read it your co worker is incorrect, unless you have some kind of an amendment.
Enjoy your read and review applicable code sections.
I know sometimes artical 250 seams to be confusing however don't read more into it than what it says.
Soares is a great source of info on the subject. I would get the book and read thought it. It helped me a lot with artical 250.
It will guide you though the calculations you seek. It also holds the key to your question on 250.122 is set up.
There is a paper that called history of residential grounding. Search this and read. I think you find it interesting. It dates way back as the code was developed.
Here is an insert from the paper. As you read though it you find key items that directly relate to today's NEC code on grounded systems.
I know I like learning so I hope you enjoy.
The first one was in 1999 and the second in 2010. I didn't provide the lugs. Incoming was about 3/0 CU
What difference does it make? If the EGC lug in the fire pump controller won't accommodate the size of EGC being installed, you simply replace the lug.Do you know the fire pump ground lug size in those?
Doesn't matter, the electrician can supply whatever he/she needs.Do you know the fire pump ground lug size in those?
What difference does it make? If the EGC lug in the fire pump controller won't accommodate the size of EGC being installed, you simply replace the lug.
Contact the manufacturer for your answer.Not fire pump controller the Fire pump itself.
Difference is in listed equipment changing lug may invalidate the listing. Its like changing what manufacturer provided