1793
Senior Member
- Location
- Louisville, Kentucky
- Occupation
- Inspector
You have a much bigger concern.
That is you are putting a recessed fixture in a fire rated ceiling. You have to box around the fixture with two layers of 5/8" sheetrock. Or they do make a fire rated cap that I've used before. But they're about $200 bucks per fixture. The switch in the fire rated wall cannot be within two feet of an outlet on the other side of the wall.
The ceilings to my knowledge are not considered Fire rated.
The switch box will need to be connected to a structural member like a stud. You cannot install a style of box that is only supported by the sheetrock.
That is what I thought, I just did not have the resource available to me at this time to reference.
This does not sound like a true "Fire Wall", this sounds like a fire rated partition or assembly. You will be penetrating one side only which means you will only be penetrating the "memberane" of the assembly, not through the entire assembly itself. There is a difference with how they are handled.
So would I still need to support the new box(s) to the structure? I think yes.
Here's a link from 3M that is very informative.
Great link, thanks
Anyway most of the high rises around here - at least the newer ones have PT slabs that act as the deck above - poured in pendant boxes - and intumesant paint... The rooms and halls often have a soffeted area for HVAC - sometimes as parts rocked off as plenum - and you can add any cans you want - no additional measures... (Except in the plenum...) And always rocked off from common areas and other units...
The walls however are a different story. Usually inner tenant walls can be treated as normal. But any partitions between units, or common areas are 1-2 hour rated.
Anyway - the building managment IMO is usually pretty intimate with the fire protection measures and wall/cieling ratings of their building - I ask 'em. Sometimes a good way to start a relationship for more work..
I'll check that out thanks.
I have been told that wall I am planning on getting power from does NOT back up to another Unit but It backs up a stairwell.
If there is no electric on the other side and or no power within 24" then do I still need to use Putty Pad on the metal box for the switch?