First time generator and ATS hookup

Merry Christmas
Status
Not open for further replies.

nickelec

Senior Member
Location
US
I'm going to be installing a natural gas generator for a buddy but I never did one before it's a generac generator with ats I'm pretty sure I'm ok with wiring the line and load off the meter etc but in familiar with the control wiring if any can anyone she'd some light or some.advice on this install

Sent from my SM-G950U using Tapatalk
 

nickelec

Senior Member
Location
US
Here are some pics of ats
c41534f82ced15bc4dd45c6b91d3a68e.jpg
0a95f6e7f2787f7656ac02ce83b482ce.jpg
bf58ab692422d938f45a68791ebd3848.jpg


Sent from my SM-G950U using Tapatalk
 

nickelec

Senior Member
Location
US
The home was wired with the thought if adding a generator in the future but I have not gone in to see what exactly was installed

Sent from my SM-G950U using Tapatalk
 

Joe Villani

Senior Member
I'm going to be installing a natural gas generator for a buddy but I never did one before it's a generac generator with ats I'm pretty sure I'm ok with wiring the line and load off the meter etc but in familiar with the control wiring if any can anyone she'd some light or some.advice on this install

Sent from my SM-G950U using Tapatalk

Read thru the transfer switch manual. You'll be able to figure it out. Pretty straight forward.


https://www.electricgeneratorsdirect.com/manuals/rts_inst_man_2013.pdf

Joe Villani
 

nickelec

Senior Member
Location
US
Is there anything else that's needed like an extra contactor or relay I've red some older thread's and this was discussed I'm not sure if it was in regards to a certain setup or add on


Sent from my SM-G950U using Tapatalk
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Is there anything else that's needed like an extra contactor or relay I've red some older thread's and this was discussed I'm not sure if it was in regards to a certain setup or add on


Sent from my SM-G950U using Tapatalk

That would be necessary only if the generator isn't sized to power all the house loads, including in-rush for things like air conditioning. Then you would need to shed loads using relays designed for this purpose.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
First time generator and ATS hookup

Is there anything else that's needed like an extra contactor or relay I've red some older thread's and this was discussed I'm not sure if it was in regards to a certain setup or add on


Sent from my SM-G950U using Tapatalk

That’s a generac “smart switch”.

You can connect the HVAC units to those built-in relays for load-shedding. You just need two wires to intercept the power from the t-stat.

Generac makes a wireless 50A load-shedding relay that will sync up to this ATS for other loads like the water heater, range, dryer, etc. you can install them at the appliance. They’re $120/ea.

https://www.homedepot.com/p/Generac-SMM-Smart-Power-Management-Module-6873/206643494

Sent from my iPhone using Tapatalk
 

SceneryDriver

Senior Member
Location
NJ
Occupation
Electrical and Automation Designer
Is there anything else that's needed like an extra contactor or relay I've red some older thread's and this was discussed I'm not sure if it was in regards to a certain setup or add on


Sent from my SM-G950U using Tapatalk

Many ATS's now have the ability to control the HVAC system's call for the air conditioner compressor. They do this by intercepting and controlling the 24VAC out to the compressor starter. This is done for two (and possibly three) reasons:

1) to keep the inrush from a running AC compressor from loading the generator along with all other loads in he house when the ATS transfers to the genny. It will allow the compressor to run once other loads have transferred and the generator is running them.

2) the ATS will keep the compressor off for approximately five minutes after transfer (from or back to utility power), to ensure the compressor isn't short-cycled by the quick off-on that transferring creates; it prevents damage to the compressor.

3) (possibly) set up to shed loads, including AC compressor, if the generator becomes overloaded.


It's supposed to be optional to hook this feature up, (at least on Millbank genny/ATS setups) but it's cheap insurance against a damaged AC compressor and/or stalled generator.


SceneryDriver
 

nickelec

Senior Member
Location
US
So it looks like the ats I have has a separate m module in it for AC hook up .do the AC load circuits need to be hooked up to this and the 24 volts as well?

Sent from my SM-G950U using Tapatalk
 

nickelec

Senior Member
Location
US
Problem is the thermostat is pretty far from where the Ats will be mounted

Sent from my SM-G950U using Tapatalk
 

Knuckle Dragger

Master Electrician Electrical Contractor 01752
Location
Marlborough, Massachusetts USA
Occupation
Electrical Contractor
That’s a generac “smart switch”.

You can connect the HVAC units to those built-in relays for load-shedding. You just need two wires to intercept the power from the t-stat.

Generac makes a wireless 50A load-shedding relay that will sync up to this ATS for other loads like the water heater, range, dryer, etc. you can install them at the appliance. They’re $120/ea.

https://www.homedepot.com/p/Generac-SMM-Smart-Power-Management-Module-6873/206643494

Sent from my iPhone using Tapatalk

What a great idea. Has it been reliable in the applications you installed them in?
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
So it looks like the ats I have has a separate m module in it for AC hook up .do the AC load circuits need to be hooked up to this and the 24 volts as well?

Sent from my SM-G950U using Tapatalk

You only need two wires for make/break of the 24v line; you don’t have to go to the t-stat, you can intercept it at the unit.


Sent from my iPhone using Tapatalk
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
What a great idea. Has it been reliable in the applications you installed them in?

Yes..... no idea how they actually sync themselves to the generator though. I’ve always been curious what would happen if you had a nearby ATS at a neighboring house.

They automatically shut off when standby power comes on for up to 5 min, and then the ATS will signal them to close if not overloaded.


Sent from my iPhone using Tapatalk
 

SceneryDriver

Senior Member
Location
NJ
Occupation
Electrical and Automation Designer
Problem is the thermostat is pretty far from where the Ats will be mounted

Sent from my SM-G950U using Tapatalk

18-2 thermostat wire is cheap; you only have to break the 24VAC control line. It's not necessary to break the power conductors to the AC compressor.


SceneryDriver
 

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
Yes..... no idea how they actually sync themselves to the generator though. I’ve always been curious what would happen if you had a nearby ATS at a neighboring house.
They automatically shut off when standby power comes on for up to 5 min, and then the ATS will signal them to close if not overloaded.

Based on my reading of the manual for the device, there is no signalling or connection of any type between the smart module and the ATS. (There is no radio signal.) The smart module just monitors the genny frequency and sheds the load if the genny goes below 58 hz for 3 seconds. This means all of the installed smart modules (up to 8) will shed simultaneously. They will reconnect the load after a time delay (if the genny is running above 58 hz). The time delay is determined by the priority setting. No two devices are supposed to be set to the same priority. Priority 1 reconnects after 5 minutes and each priority after that is delayed by an additional 15 seconds. Based on this, you could use these smart modules with any brand of ATS or even a manual TS.

ETA: They can be installed anywhere you can intercept the circuit. At the panel seems most convenient, but they can be installed next to the device as well. The case is NEMA 3R and there are 1/2" KO's. They only work with 240V loads. Not sure why you would want to shed a 120v load, but somebody at Home Depot's site asked this question.
 
Last edited:

GMc

Senior Member
Based on my reading of the manual for the device, there is no signalling or connection of any type between the smart module and the ATS. (There is no radio signal.) The smart module just monitors the genny frequency and sheds the load if the genny goes below 58 hz for 3 seconds. This means all of the installed smart modules (up to 8) will shed simultaneously. They will reconnect the load after a time delay (if the genny is running above 58 hz). The time delay is determined by the priority setting. No two devices are supposed to be set to the same priority. Priority 1 reconnects after 5 minutes and each priority after that is delayed by an additional 15 seconds. Based on this, you could use these smart modules with any brand of ATS or even a manual TS.

ETA: They can be installed anywhere you can intercept the circuit. At the panel seems most convenient, but they can be installed next to the device as well. The case is NEMA 3R and there are 1/2" KO's. They only work with 240V loads. Not sure why you would want to shed a 120v load, but somebody at Home Depot's site asked this question.

I originally thought it just sensed the frequency until I viewed the flow chart in the manual. Shortly after the module powers up it checks power source utility/generator. see attached
 

Attachments

  • flow chart.jpg
    flow chart.jpg
    9.6 KB · Views: 6

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Based on my reading of the manual for the device, there is no signalling or connection of any type between the smart module and the ATS. (There is no radio signal.) The smart module just monitors the genny frequency and sheds the load if the genny goes below 58 hz for 3 seconds. This means all of the installed smart modules (up to 8) will shed simultaneously. They will reconnect the load after a time delay (if the genny is running above 58 hz). The time delay is determined by the priority setting. No two devices are supposed to be set to the same priority. Priority 1 reconnects after 5 minutes and each priority after that is delayed by an additional 15 seconds. Based on this, you could use these smart modules with any brand of ATS or even a manual TS.

:thumbsup: couldn't have said it any better

Remember the prime mover is only going to have a rating about the same as the generator, at is nears full load it is going to slow down a little - that is when frequency will drop.

This concept would not necessarily work on an inverter output unit though.
 