please do not dismiss me because of my age i did not get to where i am today just because of my cute looks or family prestige, like my sister who also graduated higher education i have also recently done so. i have two masters degrees one in electrical engineering and one in information technology data center management. i have also recently moved to the united states from Sapporo japan. now i will get to the point.
the public utility here is Puget sound energy.
i am used to dealing with utility company's on power quality issues and other things. but this has me flustered.
the site i am working is a small data center, aprox 1,870 Sqf served by a 200A 1 phase 120/240 volt service via overhead drop.
the site has all new wiring and load-centers (cuttler hammer)
the poco says that the service drop is sized properly but, why is a load as small as 7.8 amps able to bring down one leg of the service the service drop is 2/0 alum. the feeder between load centers is 3/0 copper with a length of 54 feet +- 3 feet.
with a load of 11.7 amps applied to one leg i can bring the voltage as low as 109 volts on that leg. this is mirror on the opposite leg if i apply the load to it . moving on to the 100A sub panel feed from this 200A mains i can cause the legs to swing a symptom of a bad neutral that is also present at all the load centers. this service has been replaced from the service drop to the meter base clean back to the sub panel. 1 year ago and i have myself inspected the entire system and found all lugs and components to be in proper order with no damaged stranding or other faults that would cause the, unbalance to be present or such a high fop. am i correct in my conclusion that the overhead line between the pot and service head is bad or that the transformer itself has a bad connection inside it? the poco has remade the splices on this service drop 3 times with the same issue remaining.
the public utility here is Puget sound energy.
i am used to dealing with utility company's on power quality issues and other things. but this has me flustered.
the site i am working is a small data center, aprox 1,870 Sqf served by a 200A 1 phase 120/240 volt service via overhead drop.
the site has all new wiring and load-centers (cuttler hammer)
the poco says that the service drop is sized properly but, why is a load as small as 7.8 amps able to bring down one leg of the service the service drop is 2/0 alum. the feeder between load centers is 3/0 copper with a length of 54 feet +- 3 feet.
with a load of 11.7 amps applied to one leg i can bring the voltage as low as 109 volts on that leg. this is mirror on the opposite leg if i apply the load to it . moving on to the 100A sub panel feed from this 200A mains i can cause the legs to swing a symptom of a bad neutral that is also present at all the load centers. this service has been replaced from the service drop to the meter base clean back to the sub panel. 1 year ago and i have myself inspected the entire system and found all lugs and components to be in proper order with no damaged stranding or other faults that would cause the, unbalance to be present or such a high fop. am i correct in my conclusion that the overhead line between the pot and service head is bad or that the transformer itself has a bad connection inside it? the poco has remade the splices on this service drop 3 times with the same issue remaining.