status update
status update
i have for the time fixed the issue by moving all the 120V loads to one leg leaving only the 240V loads tied to the two they are not as picky about the bad leg issue. the house on the other side of the street has all electric heat whenever a 240 V load throws in there is a noticable change in the l-l voltages one leg at both services drops from 121.75V rms to between 114.18 and 113.27V rms. the other leg (B phase or L2) remains steady at 121.52-120.17V rms but if a 120 load throws in on L1 A phase both are all over the place.
so i moved al the 120 loads to the B phase and switched all the pem's to 240V and am simply going to wait for the poco transformer to fault of its own doings as this is a transformer issue not a service drop issue.
status update
i have for the time fixed the issue by moving all the 120V loads to one leg leaving only the 240V loads tied to the two they are not as picky about the bad leg issue. the house on the other side of the street has all electric heat whenever a 240 V load throws in there is a noticable change in the l-l voltages one leg at both services drops from 121.75V rms to between 114.18 and 113.27V rms. the other leg (B phase or L2) remains steady at 121.52-120.17V rms but if a 120 load throws in on L1 A phase both are all over the place.