They just have 1/2 and 3/4 knockouts. I'd think you ought to be able to use them for whatever you want to.peter d said:I've never used one but they are listed for use with MC cable too, right?
They just have 1/2 and 3/4 knockouts. I'd think you ought to be able to use them for whatever you want to.peter d said:I've never used one but they are listed for use with MC cable too, right?
mdshunk said:They just have 1/2 and 3/4 knockouts. I'd think you ought to be able to use them for whatever you want to.
No, but most old work situations are only going to have one cable anyhow. Two MC's are pretty rough to get back in the wall if you have one in each end. If you need two, you're probably going to use a duplex connector, then the bonding would remain in tact.peter d said:Right, but isn't there a metal plate in between the KO's to keep the bonding intact?
I suppose I could just look one up. :roll:
peter d said:Right, but isn't there a metal plate in between the KO's to keep the bonding intact?
I suppose I could just look one up. :roll:
Since when does a box have to be listed for a particular wiring method. Since never...raider1 said:The Arlington In-boxes that I have used don't have a metal plate to ensure bonding, so I don't think they are listed for MC cable.
mdshunk said:No, but most old work situations are only going to have one cable anyhow. Two MC's are pretty rough to get back in the wall if you have one in each end. If you need two, you're probably going to use a duplex connector, then the bonding would remain in tact.
mdshunk said:Since when does a box have to be listed for a particular wiring method. Since never...
Maybe, but they also don't feature knockouts, typically. Now you're gonna make me look up what the In-Boxes are listed under.peter d said:What about a regular plastic nail on box? Surely those are not listed for anything other than non-metallic wiring methods.
mdshunk said:Since when does a box have to be listed for a particular wiring method. Since never...
iwire said:I agree and think this issue is covered by 314.3 Exception 1 if you really wanted to enter MCs into the box.
peter d said:Well there you go again, you make everything simple to understand by quoting code.![]()
mdshunk said:Since when does a box have to be listed for a particular wiring method. Since never...
If you only have one cable, it doesn't matter anyhow. If you need two, use a duplex connector. So far, this is the only box that I've found that you can compliantly use in old work rated assemblies without having to do a pretty serious repair on the wall.
Sure you could. You could use a duplex connector for two. The box has three knockouts. If you wanted to go hog-wild, you could use a duplex connector in each knockout, put a bond-bushing on all three, and connect them up, for a total of 6 mc's .raider1 said:I apologize for using the term "listed" for a particular wiring method. What I ment to say is that with the design of the arlington in-box you could not use multiple MC cables.
Chris
Yeah, the UL guide talks about that under the "clamps" heading. The clamps are what are identified for a particular use.iwire said:I think the labeling on those may indicate NM only.
mdshunk said:Sure you could. You could use a duplex connector for two. The box has three knockouts. If you wanted to go hog-wild, you could use a duplex connector in each knockout, put a bond-bushing on all three, and connect them up, for a total of 6 mc's .
Yeah, but I was just being extreme to make a point. One duplex connector is all you could manage to get in the wall. I had a few of those 45-degree duplex connectors a while back. I wonder if they still make those? I bet they'd work even better. There is a KO dead centered in the back you could use a right angle connector in, but conductors coming in the back make for a tough makeup, in my opinion.peter d said:But then you would have to surface mount it.![]()
mdshunk said:Yeah, but I was just being extreme to make a point.
Yeah, that's viable, but scroll back a couple posts:LLSolutions said:what about just using a 90 connector into the back k/o?
mdshunk said:...There is a KO dead centered in the back you could use a right angle connector in, but conductors coming in the back make for a tough makeup, in my opinion.