If I'm using 12/2 mc instead of factory whips, can they be in lengths longer than 6 ft?

Sent from my LG-D850 using Tapatalk
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
They can be as long as the spool you buy.

Roger
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
12/2 on a 20 amp circuit would be an extension of the branch circuit so there is no length limit as Roger stated.
 

kwired

Electron manager
Location
NE Nebraska
You must still support the cable within 6 feet (of cable length) of the luminaire.

For example you could not make a drop to a lay in fixture from a box located 10 feet above it with no additional cable supports.
 