C cymro80 New member Sep 27, 2015 #1 If I'm using 12/2 mc instead of factory whips, can they be in lengths longer than 6 ft? Sent from my LG-D850 using Tapatalk
If I'm using 12/2 mc instead of factory whips, can they be in lengths longer than 6 ft? Sent from my LG-D850 using Tapatalk
roger Moderator Staff member Location Fl Occupation Retired Electrician Sep 27, 2015 #2 They can be as long as the spool you buy. Roger
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Sep 27, 2015 #3 12/2 on a 20 amp circuit would be an extension of the branch circuit so there is no length limit as Roger stated.
12/2 on a 20 amp circuit would be an extension of the branch circuit so there is no length limit as Roger stated.
kwired Electron manager Location NE Nebraska Occupation EC Sep 27, 2015 #4 You must still support the cable within 6 feet (of cable length) of the luminaire. For example you could not make a drop to a lay in fixture from a box located 10 feet above it with no additional cable supports.
You must still support the cable within 6 feet (of cable length) of the luminaire. For example you could not make a drop to a lay in fixture from a box located 10 feet above it with no additional cable supports.