recently had a person request that the appliance plug(male end) be changed from a 20 amp to a 30 amp so they can plug into their 30 amp receptacle .
Had to tell them that is a Code violation, and that its not allowed. She said all the 'other' equipment in their shop was changed this way in the passed and they just wanted to make everything the same.
YIKES!!
I say "Even though the cord plug is going only to that appliance and its likely the load will not increase on that cord/plug , Only the manufacturer can get away with this type of install because of the ocpd can be used in this manner, NEC 2005 400.13. If a electrician alters that, then there can be liability. "
So did I handle this correctly (tried to be as nice as possible). Any other articles you can throw at this??
Had to tell them that is a Code violation, and that its not allowed. She said all the 'other' equipment in their shop was changed this way in the passed and they just wanted to make everything the same.
YIKES!!
I say "Even though the cord plug is going only to that appliance and its likely the load will not increase on that cord/plug , Only the manufacturer can get away with this type of install because of the ocpd can be used in this manner, NEC 2005 400.13. If a electrician alters that, then there can be liability. "
So did I handle this correctly (tried to be as nice as possible). Any other articles you can throw at this??