Nope, I 'm not saying one rod was not enough it may very well have been.sparkygriffin said:Now were getting somewhere. If you agree that one ground rod isn't going to be enough than his house was not meeting the NEC.
As far as being code compliant, the first rod may have had a resistance of 1000 ohms and adding a second rod would probably not have lowered the GE resistance much if anything at all but, we would still be code compliant.
The 25 ohm requirement is only for one rod, if that can not be met you add the second rod and your done even if the total resistance is 100,000 ohms.
No, odds are the second rod would not of changed anything.sparkygriffin said:So would you than agree that if it did he may not have expeireneced the problems he had?
Let's assume there was a GES resistance of 25 ohms between the sevice rods and the pole base ground, (the earth being the conductor between the two) any unbalanced neutral current of over 4.8 amps would be a lost cause and we would be letting smoke out of many of the items inside the house.sparkygriffin said:That was my point go back and check. I always said he had to have a good grounding system, just like the PO.CO. said.
You're welcome.sparkygriffin said:And thank you for the warm welcome.
Roger