I would appreciate it if someone could give me an example of FMT. (Flexible Metallic Tubing) Not to be confused with FMC (Flexible Metal Conduit) which I use every day in commercial applications for things such as lighting whips and such
The reason i pose this question is that i hear quite often that 'FLEX' is not allowed in lengths over six feet..
'FLEX' is FMC, and there is no such restriction (6 ft) on FMC, but there Is a 6 ft restriction on the use of FMT.
So I need an example to give when someone tells me that i cannot use 10 feet of aluminum 'FLEX' to fish down a wall....