strong arm torque specs are "tighten er down til ya hear it pop, then back er off a quarter turn"
Huh? Who's saying to torque the conductors live?dcspector said:I will stay out of this one Marc.....We have had this debate before as far as live work......remember?:smile:
Hmmm... haven't torqued any busbars with large bolts lately, huh?busman said:... The largest torque I remember using was 300 in-lb which is 25 ft-lbs. Most wrenches marked in ft-lbs will not measure that low.
Since you said this was overseas stuff, did it not use Bellville washers, maybe? I notice the torque spec often does seem higher on bus connections without Belleville washers or Belleville-type nuts.Smart $ said:As I recall, when converted the torque spec'd for largest bolt size used (M16, I think) was over 100 ft-lbs.![]()
That is correct. No belleville washers or nuts.mdshunk said:Since you said this was overseas stuff, did it not use Bellville washers, maybe? I notice the torque spec often does seem higher on bus connections without Belleville washers or Belleville-type nuts.
I'd gripe, too.mdshunk said:My present gripe is with the bus connections in Milbank ganged meter sockets. They strip out about 2 pounds beyond the torque spec. No nuts on the back side. The two overlapping sections of bus have the front piece with a clearance hole and the back piece with a tapped hole, and it's all aluminium.
Beats me, but that's how I fix 'em. The bolt is long enough.Smart $ said:Would it be a violation to put jam nuts on the backside?
It was at that point that I realized that I didnt want a pickle I just wanna ride my motorcycle. ONLY THE OLDER GUYS will remember this one. Arlo Guthriestuartdmc said:I ran a 225amp feed 400ft with (2) 2?conduits - 4 #2/0 THHN copper each, to a 225 amp dock powered pedestal. To prevent an extreme voltage drop I up sized my wire and ran parallel runs. The problem is that I have installed my OCPD in line prier of going down to the dock , and now, I am finding out that the 225A circuit breaker within the Disconnect will not accept two 2/0 wires or double lugs. So, what I?ve done is, I?ve cut in a junction box to tap and extend each conductor, both line and load with a single 4/0 wire going too and from the circuit breaker. This connection is made using a ?Greave? connector rated for 250kcmil to a # 6 AWG.
This is what the inspector needs to see the torque on as well as the circuit breaker,
Oh, the main 225A circuit breaker won?t accept the two wire?s as well.
quogueelectric said:It was at that point that I realized that I didnt want a pickle I just wanna ride my motorcycle. ONLY THE OLDER GUYS will remember this one. Arlo Guthrie
Belleville washers are concave spring steel, aren't designed to be fully colasped, wouldn't provide full area contact and wouldn't provide a solid connection. Belleville nuts? Sure you don't mean a skirted nut, a nut with a built in washer?mdshunk said:Since you said this was overseas stuff, did it not use Bellville washers, maybe? I notice the torque spec often does seem higher on bus connections without Belleville washers or Belleville-type nuts.
My present gripe is with the bus connections in Milbank ganged meter sockets. They strip out about 2 pounds beyond the torque spec. No nuts on the back side. The two overlapping sections of bus have the front piece with a clearance hole and the back piece with a tapped hole, and it's all aluminium.
I didn't think that you'd want a springy connection but, heck, I'm not a electrician! In that case, torque specs would be very important.iwire said:![]()
Belleville Washer Nut
Large flange distributes torque load and restricts compression of material.
Spring steel washer maintains surface contact as material expands and contracts.
Prevailing torque remains high even when connection is subject to vibration.
From here
wptski said:I didn't think that you'd want a springy connection but, heck, I'm not a electrician!
Have seen spring washers 2"-3" in diameter used in a huge stack! Talk about clamping force.iwire said:'Springy' hardware is commonly used for bolted electrical connections. The spring is intended to maintain the same clamping force regardless of the expansion and contraction of the material. :smile:
I disagree, mainly because there was a period of time when ITE switchgear came with alternate torque instructions to tighten the bolts until the Belleville washer flattened, then back off 1/4th turn (the washer was still pretty much flat when you backed off). The Belleville washer isn't the contact area anyhow. The bus-to-bus contact area is what matters. The Belleville washer just keeps tension on the connection through heating and cooling cycles.wptski said:Belleville washers are concave spring steel, aren't designed to be fully colasped, wouldn't provide full area contact and wouldn't provide a solid connection.
You were adusting the Belleville washer to be within it's spring range then. If it was a seperate piece, they could have you rotate it till washer made contact and so much of a turn tighter after that.mdshunk said:I disagree, mainly because there was a period of time when ITE switchgear came with alternate torque instructions to tighten the bolts until the Belleville washer flattened, then back off 1/4th turn (the washer was still pretty much flat when you backed off). The Belleville washer isn't the contact area anyhow. The bus-to-bus contact area is what matters. The Belleville washer just keeps tension on the connection through heating and cooling cycles.
I'll have to take your word on that.wptski said:It's like adjusting hydraulic lifters on a gas engine, with it running hot, you loosen till they start clacking or zero lash and tighten so many turns down to what the specs were.