mayjong said:isn't a connection buried in concrete now "irreversible"?
Obviously you have never seen Florida drivers! :smile:
mayjong said:isn't a connection buried in concrete now "irreversible"?
I say no to both. 5' of #4 connected to rebar is not a grounding electrode. It is a grounding electrode conductor. If it is too short to reach the disco, you need an irreversible connector to add more wire.hillbilly said:I'm not talking about the connection to the re-bar, that's OK.
I'm talking about the connection of the (#4) GEC that runs from the panel to the other piece of #4 that goes into the footer.
I'm asking if the piece of #4 wire that goes into the footer is part of the grounding electrode and if I can connect to it with a (listed) split bolt?
I say yes to both.
steve
rcarroll said:I say no to both. 5' of #4 connected to rebar is not a grounding electrode. It is a grounding electrode conductor. If it is too short to reach the disco, you need an irreversible connector to add more wire.
infinity said:I agree unless you have a metallic water pipe too. Then the GEC would go to the water pipe. The conductor to the CEE would be a bonding jumper.
bphgravity said:also require a new mono-slab CEE installed to be run to the new service.
Bea said:I disagree this has been discussed before but the CEE is a grounding electrode by difinition the conductor that connects it to the service equipment is a GEC by definition not a bonding jumper.
infinity said:If there is a metal water pipe present then the conductor connected to it would be the GEC. The CEE would be the supplemental electrode which is connected by a bonding jumper not a GEC.
celtic said:I missed the inspector, but the GC asked him the same questions I had:
Q: What's the point?
A: I don't know..I'm just here to enforce the code.
Inspite of all this..I still fail to see "What's the point?"
gndrod said:Other than saving time and material costs on residential & multi-family installations, plastic water supply pipe that the plumber or well sub may decide to install later. Note that #4 rebar (1/2") is minimum UBC, IRC for foundation footers. #3 is used along horizontal wall cinderblock and risers only. rbj
If a conductor starts at the service and ends at a GE, it's a GEC.Bea said:I disagree this has been discussed before but the CEE is a grounding electrode by difinition the conductor that connects it to the service equipment is a GEC by definition not a bonding jumper.