big vic said:Halo website says "IC" means insulated ceiling
CBL said:My source is a guy at the Home Depot, so take it for what it's worth...
macmikeman said:IC recess cans look almost the same as non IC cans except for a flat plate inside that reflects heat back out the opening of the can. If you look in the opening and no flat plate at the base where the lamp socket is then it is a non IC can. There is that earth shaking difference and one other. The other difference is that the stickers are different. One says IC and the other says non IC. Both types have a thermal cutout since I don't remember exactly when, I think it was in the early to mid 80's when I started seeing them. The recess cans with the square box look are serving another purpose - sealing for keeping cold air out and warm air in the room. Those types are mostly rated IC also.
You have to look at the label inside the can. It will tell you what bulbs you can use with a respective trim. A shower trim used with an IC can will usually restrict you to a 40 watt A bulb. In the case of an eyeball trim you'll have to remove the socket from the top plate and remove the plate altogether because the trim has an articulating part. But again, you'll have to read the instructions inside the trim or find a cut sheet that explains what trims you can use.monkey said:So does this mean when you change to a trim like a shower trim or an eyeball trim which requires you to remove that flat plate and install the socket directly into the new trim, you now have a non IC rated can?
These are usually ICAT cans but I don't know if all manufacturers make them with a 1/2" space between the layers.monkey said:And I thought IC cans had a double construction on top with a 1/2 inch air space between the layers.
The insulation may completely encapsulate the can.knightstar said:Can the IC rated recessed light have insulation over the can or is the in-contact considered to only be associated with being in-contact with the perimeter of the recessed light housing.
LarryFine said:The insulation may completely encapsulate the can.
Dennis Alwon said:Totally illegal because there is no way to access the wiring.
celtic said:Where/what is the requirement for wiring to be "accessible"?
Don't the cans have an access plate that can be reached (if you're a contortionist) from inside the housing?Dennis Alwon said:The splice in the JB must be accessible. You can't bury a box in the wall--- you know that. That is why the cans are removable so you can get access to the box. If it is glued in this foam you can't get to it.
celtic said:Don't the cans have an access plate that can be reached (if you're a contortionist) from inside the housing?
EDIT:
I didn't see until I typed it....LOL....the foam is ALSO now if the way of that so-called access.
Dennis Alwon said:Have you all not seen this in NJ yet. It's been on three or four jobs lately.
Dennis Alwon said:Right, the box is encapsulated with foam. Have you all not seen this in NJ yet. It's been on three or four jobs lately. I'll tell you something. No more leaving the wall stubbed out for lights--- you better cut them in before they blow that S... in there.