The CEE and the building steel could certainly be bonded together. One problem though is the EI did not see it before it was encased so he still doesn't know if they are bonded or not.
Certainly.
The CEE and the building steel could certainly be bonded together. One problem though is the EI did not see it before it was encased so he still doesn't know if they are bonded or not.
No.
"Metallic components shall be encased by at least 50 mm
(2 in.) of concrete and shall be located horizontally within that
portion of a concrete foundation or footing that is in direct
contact with the earth or within vertical foundations or structural
components or members that are in direct contact with
the earth. If multiple concrete-encased electrodes are present
at a building or structure, it shall be permissible to bond only
one into the grounding electrode system."
I have known of AHJs that make the contractor dig down and cut into the foundation to make the connection. Saying "I forgot" doesn't cut it.
Keep in mind the OP is in Turkey.
Since it is impossible to determine if the construction meets the requirements for a CEE, I'd say skip it and drive a couple ground rods and be done with it. Assuming that they are actually using NFPA 70 as their standard and the OP isn't just looking for opinions on what might be considered simply good practice.
There is another perspective on this topic.Keep in mind the OP is in Turkey.
Since it is impossible to determine if the construction meets the requirements for a CEE, I'd say skip it and drive a couple ground rods and be done with it.
Why? How does a better path to Earth serve any useful purpose?
Seems like that kind of was his point.Why have a path if it is so insignificant to you?
If you can only get 100 ohms with two rods chances are you aren't getting down to only one ohm with the CEE, unless it is a really large CEE. But I also agree that it really doesn't matter. Inspectors get fixed on the importance of a GES, when in reality unless you are not connected to a utility system with many grounding electrodes connected to it, one missing electrode at one service isn't as big of a deal as they want it to be.
Areas with a high level of lightning incidents maybe it becomes somewhat higher importance though.
Seems like that kind of was his point.
I don't have a problem with having a path regardless of how good or bad that path is, but don't see it being as critical as some think it is. Bonding of non current carrying components is much more important then grounding. You can't expect the earth to reliably carry current for under 1000 volts applications.
Now enter the lightning strike with extremely high voltage and high frequency components, that electrode that only has 100 ohms impedance still looks like a low impedance, and you may not have much difference in damages even if that electrode were 10 ohms.
I see that OP is in Turkey, and they are quoting NEC as requirements.
The UFER is proven to be less resistance in nearly all instances then a ground rod. Or two, or three, or maybe even a hundred.did you opine or is that your scientific study -- the military whom designed the UFER may disagree.
it only takes one lighting strike to cause damage -- I've seen it
So have I, with structures that have grounding electrodes as well as those that don't.it only takes one lighting strike to cause damage -- I've seen it
The UFER is proven to be less resistance in nearly all instances then a ground rod. Or two, or three, or maybe even a hundred.
That has nothing to do with whether presence of a grounding electrode of any resistance actually benefits the building or structure.
The military did not design the UFER. Herbert G. Ufer was a consultant working for the U.S. Army, and they wanted him to find a better method to protect bomb storage vaults from lightning strikes then ground rods provided - particularly in the southwest desert.
This original intent had little to do with electrical systems and a lot to do with lightning protection.
So have I, with structures that have grounding electrodes as well as those that don't.
Grounding electrode on the electrical system is not the same thing as a lightning protection system.
a
true but the purpose follows the same path -- is lighting protection a better path to earth?????
Interestingly, I searched for a national electrical code for Turkey and couldn't find anything. There was some reference to the use of ad hoc standards based on the project specifications. So, my question remains: is this actually a requirement or is the engineer just trying to do his best without having the benefit of an actual local standard?
Some of what you have in quotation marks is what I said and some of it is changed from what I said??"The UFER is proven to be less resistance in nearly all instances then a ground rod. Or two, or three, or maybe even a hundred." comparing to 100 rods seems significant.
"military did not design the UFER. Herbert G. Ufer was a consultant working for the U.S. Army," ???( the army is not military ?)
"This original intent ( electronic malfunction protection) had little to do with electrical systems ??? and a lot to do with lightning protection" ( again the grounding electrode system primary objective is to protect electrical system damage from high voltages induced from lighting strikes by aiding its path to earth to be absorbed -- have seen the results of a home burned down with the conclusion of faulty install of electrode system, the copper staple to the exterior absorbed so much energy it ignited the wood siding on fire. quite a bit of the insulation on NM was compromised and had to be replaced.
We certainly do have different values for the electrode system and its importance. You seem to be on a scale of 1 to my 9.
a
true but the purpose follows the same path -- is lighting protection a better path to earth?????
The site is located in middle east and the designers in turkey. however, the project does have a requirement to meet the NEC. and turkey does have local standards similar to the European ones:"TS/EN"
Since apparently we've wandered into lightning protection I'm not too concerned with exacerbating thread drift. Thank you for clarifying that the project has a specific requirement to meet the US NEC. I did see references to the TS/EN standards at a couple of Turkish sites, but nothing that I could pin down as an electrical standard. Out of curiosity, do you have a link to the current Turkish national or local standards for electrical installation similar to the US NEC?
Q1. Regarding foundation earthing. There is no requirement to specifically design a foundation to act as a CEE. If you used fiberglass rod for rebar, or the rebar was plastic-coated, or there was a moisture barrier (ie, plastic sheeting) under the slab, all these things would prevent you from having a CEE or Ufer system. You could look at NFPA 70-2014 250.50(A)(4) as a possible solution (grounding ring) if there is a concern.
Now if, and only if, the foundation reinforcement meets the requirements to be a CEE, you will have to expose the rebar somehow and cadweld a connection to it or use some other approved method.
Q2. You can still use an exothermic weld to make the connection. As others have pointed out, there are other ways to get it done that are acceptable and that may or may not be easier to execute.