Re: Freak Accident:
Hi I am a new guy here and I am not an electrician. I signed up because I am on a sound guy Forum (Churchsoundcheck.com) It is a Forum for church sound guys and as you can imagine, we have been very interested in the tragic accident of the pastor who was electrocuted in a baptismal.
I am writing to provide a little information on the sound system side of things.
First Phantom power. Phantom power was correctly pointed out as power provided to condenser mics. It is from 11 to 48 volt DC It is current limited (suppled from the power supply often through a 6810 ohm resistor. It is suppled equally to BOTH sides of the audio pair.
http://www.tangible-technology.com/power/Phantom_Power_connect.html
It must be suppled through high value resistors because otherwise it will short out the audio. A conventional microphone (Non condenser) has a coil across the pair of audio lines running in a shielded cable. Because it is across this pair with + 48 VDC on both wires it doesn't see it' and therefor is not damaged. If the mic is condenser then it gets it's DC power from the difference between the shield and the two audio wires.
A great many mics used in churches are Condenser and need phantom power. In the church where I run sound all the mics need phantom power (about 14 mics ) The only exceptions are the two wireless mics we use.
A good Condenser mic can cost as little as $35
Most (but not all) equipment that plugs into a microphone jack is not harmed by phantom power.
The less expensive boards will have only one switch to supply phantom power to all mics.
Grounds. On the Churchsoundcheck Forum we are nuts about safety grounds. You don't get to mess with them, You will get yelled at big time if you do. Safety grounds do cause us problems because they can form a ground loop (current flow in the shield of audio cables. We solve this problem by installing isolation transformers. When the transformer provides impedance matching and isolation it is called a Direct Box (often used between a guitar pickup, and a microphone line. These boxes allow us to couple the audio but not the ground. We will also some times use a cable with the shield disconnected from the plug at one end. (Remember, this shield is not a safety ground but a audio signal ground.)
In some cases it is necessary to wire or rewire a facility with a isolated star safety ground system. (The safety ground from a outlet doesn't connect to the separate ground on the box until they get back to the panel.) For this, of course, we need to use the services of an electrician. It can be interesting to find one who understands why we are so nuts not just about grounding, but about how the outlets are grounded.
I hope this info helps you thick wire guys understand some of us thin wire guys. I would like to be able to come back and ask you some questions when we get into safety issues on our forum
BTW We use a wireless mic mounted on a stand for our baptismal. Before this accident we had the pump and heater on a big knife type disconnect, with directions to turn them off before people entered the baptismal. The baptismal is grounded (The church was built in the early 60s) now we have that plus GFI
Frank DeWitt
Hi I am a new guy here and I am not an electrician. I signed up because I am on a sound guy Forum (Churchsoundcheck.com) It is a Forum for church sound guys and as you can imagine, we have been very interested in the tragic accident of the pastor who was electrocuted in a baptismal.
I am writing to provide a little information on the sound system side of things.
First Phantom power. Phantom power was correctly pointed out as power provided to condenser mics. It is from 11 to 48 volt DC It is current limited (suppled from the power supply often through a 6810 ohm resistor. It is suppled equally to BOTH sides of the audio pair.
http://www.tangible-technology.com/power/Phantom_Power_connect.html
It must be suppled through high value resistors because otherwise it will short out the audio. A conventional microphone (Non condenser) has a coil across the pair of audio lines running in a shielded cable. Because it is across this pair with + 48 VDC on both wires it doesn't see it' and therefor is not damaged. If the mic is condenser then it gets it's DC power from the difference between the shield and the two audio wires.
A great many mics used in churches are Condenser and need phantom power. In the church where I run sound all the mics need phantom power (about 14 mics ) The only exceptions are the two wireless mics we use.
A good Condenser mic can cost as little as $35
Most (but not all) equipment that plugs into a microphone jack is not harmed by phantom power.
The less expensive boards will have only one switch to supply phantom power to all mics.
Grounds. On the Churchsoundcheck Forum we are nuts about safety grounds. You don't get to mess with them, You will get yelled at big time if you do. Safety grounds do cause us problems because they can form a ground loop (current flow in the shield of audio cables. We solve this problem by installing isolation transformers. When the transformer provides impedance matching and isolation it is called a Direct Box (often used between a guitar pickup, and a microphone line. These boxes allow us to couple the audio but not the ground. We will also some times use a cable with the shield disconnected from the plug at one end. (Remember, this shield is not a safety ground but a audio signal ground.)
In some cases it is necessary to wire or rewire a facility with a isolated star safety ground system. (The safety ground from a outlet doesn't connect to the separate ground on the box until they get back to the panel.) For this, of course, we need to use the services of an electrician. It can be interesting to find one who understands why we are so nuts not just about grounding, but about how the outlets are grounded.
I hope this info helps you thick wire guys understand some of us thin wire guys. I would like to be able to come back and ask you some questions when we get into safety issues on our forum
BTW We use a wireless mic mounted on a stand for our baptismal. Before this accident we had the pump and heater on a big knife type disconnect, with directions to turn them off before people entered the baptismal. The baptismal is grounded (The church was built in the early 60s) now we have that plus GFI
Frank DeWitt