Mvillines
- Western KY on the Ohio River
After the calibration date on the CT?s expires it?s going to be tough on the poco metering department.
Looks like the CT cabinet is not grounded to the neutral conductor. And there is no need for the EGC's in with the conductors going to the main disconnect. Once the neutral is bonded to the CT cabinet they will become ea parallel path for the neutral current.
II can't believe they make you thread the wires through the CT donuts like that, that is a royal pain! Your POCO needs to get with the program and start using bolt-in CT's like Bob posted, that's the only kind we use around here.