There are three basic types of heat tape.
1. Series, in which the resistance heating wire runs from one end of the tape to the other. It is difficult to get a significant increase in resistance over a temperature range near room temperature and definitely below 100C. So these require a thermostat and if crossed or wadded up can produce extremely high local temperatures. And if the wire gets hot enough it will cause a locally higher resistance, leading to a far higher heat density on what is essentially a constant current circuit.
2. Wire type parallel, in which short lengths of resistance wire are run from one copper or aluminum conductor to the other. This essentially puts multiple short heating elements in parallel. This will also produce excessive temperatures when crossed or wadded. But if it gets to a high enough temperature that the resistance wire increases significantly in resistance, the local heating density will decrease.
3. The self-limiting semiconductor based heat trace in which the dielectric between the two metallic conductors has a controlled resistivity designed to produce the desired heat output per length of trace. The semiconductor has a high positive temperature coefficient which is enough to drastically reduce the heat output at the design maximum temperature. Since this is also a parallel circuit, the local power density can be made quite small. But even with this there will be higher temperatures where the trace is crossed or run in parallel with itself. Not nearly as likely to start a fire though.